    Sep 2014
    Australia
    59
    1
    When is 407C not 407C, fractionation
    Hi All,
    First post here.
    When is 407C not 407C, fractionation.
    We have just done a refrigerant analysis on a 407c system that had a leak in the aircooled condenser. We lost maybe 40% of the charge. Total charge 60lb.
    407C make up is: HFC-32 (23%), HFC-125 (25%), HFC-134a (52%).
    Test results today are:HFC-32 (27%), HFC-125 (28%), HFC-134a (45%).
    This shows a 7% loss of 134a.
    AHRAE states a tolerance of +-2%? I think.
    Does this test conclusion constitute a full system re-charge?
    Cheers, Rob W
    Aug 2007
    Adelaide Australia
    70
    562
    Re: When is 407C not 407C, fractionation
    Hi Robert
    The short answer is yes. Any of the new blends that have a high temp glide (more then 1 or 2) will fractionate and cause problems if the leak is on the gas side, this is the reason for liquid charging only.
    One of the results of your above situation will probably be high discharge pressures.
    Paul
    Born to fish, forced to work
    ireland
    54
    275
    26
    Thats very interesting seen as the other gases have gone up in percentage of the mix it appears mainly the 134a was lost. Im sure there is some type of equation can be done to show exactly what percentage of each gas was lost and what needs to go back in
    Dec 2008
    564
    Still the best and simplest answer is to find and repair the leak and then start again with new refrigerant charged in the liquid phase.
    Bedford. Now retired and trying to relax.
    May 2012
    59
    1,528
    36
    R134a tends to have the smallest atoms or molecules that make up the
    whole refrigerant, that is why R134a mostly is lost first and that is
    why you lose a higher % share of it in total.
    The only people who can re-blend this is the refrigerant manufacturer,
    the chance of you adding a bit of this and a bit of that to a fractured
    blend and then getting it to the correct blend would be almost impossible.
    You have a choice then! Do you remove it all and replace it with virgin
    refrigerant or do you run the risk of adding refrigerant to the blend in the
    hope it will be OK.
    Chances are you might get away with it but if it is still blended wrong
    afterwards then you will still have to remove it all and replace it.
    I always tell anyone who asks to replace the whole lot if the total charge
    is less than 10Kg. Below 10Kg it is not worth the hassle and the risk.
    If the system is above 10Kg you, your company and the customer have
    to make a commercial decision as to whether it is worth the risk of a
    fractured refrigerant weighed against the cost of a complete regas.
    Your decision and no easy answer because you just don't know what
    state your refrigerant is before you start and what if the system had
    leaked previously and already has had extra refrigerant added.
    What on earth would be in the system is anyone's guess, unless you go
    to the expense of having it analysed.
    Rob
    Oct 2008
    newbury
    1,444
    37
    http://docs.lib.purdue.edu/cgi/viewc...&context=iracc
    all you need to show the client is in here..
    May 2012
    59
    1,528
    36
    Quote Originally Posted by r.bartlett View Post
    Interesting document.
    It shows what I thought would happen over successive leaks.
    No system is perfect but some are more prone to leaks than others
    and if you come to a fridge with 407 in it how many times before
    has it been repaired?
    If the paperwork and logs are all in place you could tell what had
    happened over the last year or so but every time you add to 407
    you dilute the mix to a point where it becomes useless to use.
    Rob
Tags for this Thread