Results 1 to 2 of 2
  1. #1
    Join Date
    Sep 2014
    Location
    Philippine
    Posts
    1
    Rep Power
    0

    Carrier 30HX Series



    Hi Engineers,

    Need help for this error "Compressor A2 Low Oil Pressure" during start-up, couldn't run my chiller.



  2. #2
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: Carrier 30HX Series

    Your chiller should still be able to run as this problem only affects A2 Compressor.
    Regarding the oil pressure problem your oil pressure is not achieving correct pressure on start up. Running oil pressure would normally be less than 80kpa below discharge pressure
    Can you put a log of running pressures for us to help you.