22-09-2014, 03:06 PM #1
Using cooling tower BAC in hard winter
Hello, sirs!
----------------------------------------------------------------------
Input data:
Сlothing manufacture. There is a nessesary in water cooling for machines.
Two water circuit.
Input water 40
Output water 23
Flow 75 cubic meter per hour
Ambient condition (following state regulatory document) in winter
temperature -31 d.C
----------------------------------------------------------------------
Basic scheme based on using
plate heat exchanger (water 40/23 / e-glycol 35% 10/17)
chiller with shell and tube condensator
dry cooler
this scheme provides free-cooling option as air temp. fall below 5 d.C
such decision requires large capital outlays, compared using air condenser.
but low energy cunsumption in winter
----------------------------------------------------------------------
BAC Baltimore suggest to use open cooling tower. Model VLT-E
i asked BAC spec about winter operation and he told about heated sump,
insulated pipes, inroom tank and fan frequency regulation
I found options of such machine in BAC sites which allow to operate above -18
but not below
----------------------------------------------------------------------
i haven`t experience with open cooling tower and have doubts that this
system will operate in -31 d.C or even -25
will be thankful for any advise or сompleted experience
sorry for my ENG
-
22-09-2014, 11:38 PM #2
Re: Using cooling tower BAC in hard winter
OK,
For what you propose to use I would say drain the cooling tower before the temperature get anywhere near freezing.
However, have you considered a hybrid cooler?
Like the Cabero range HERE.
Correctly designed they will give plenty of free cooling, have a less complicated circuit than your design (no need for the heat exchanger) and run fully automatic on their own controls.