21-09-2014, 07:11 PM #1
Daikin Nexura
Hi All, I have just installed a Daikin Nexura low level wall unit split system, The unit has a radiant front panel which heats up during heating mode and works very well, however during cooling it starts sweating and then frosts up, has anyone else seen this before ?
Skilts
-
21-09-2014, 10:58 PM #2
Re: Daikin Nexura
Does it stay frosted or does the frost clear?
Does the 'radiate' button turn off automatically when you select cooling?Brian - Newton Abbot, Devon, UK
Retired March 2015
-
22-09-2014, 05:54 PM #3
Re: Daikin Nexura
Fixed it chaps !
Took unit to bits & found solenoid valve coil laying loose in top of unit, guess it must of come off in transit,
Refitted & it works a dream,
Skilts.
-
22-09-2014, 08:27 PM #4
Re: Daikin Nexura
Is that the expansion valve or reversing valve? Nice to know what to look out for.
-
29-09-2014, 05:48 PM #5
Re: Daikin Nexura
its just a mag valve to stop gas going through radiant panel on cooling