    variable expansion valve



    Hi sirs
    Who has used the variable expansion valve as attached drawing?
    It's said to keep zero superheat for evaporator.

    rgds
    LC
    Last edited by Lc_shi; 10-04-2007 at 09:39 AM.


    I hear...I forget;I see...I remember;I do...I understand

  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: variable expansion valve

    Hi LC,

    Another interesting topic. I have not seen this before.

    One comment I would offer in regards to zero superheat. This may sound like a way to improve the system efficiency however, if the system has capacity control I can see some potential problems.

    If the compressor unloads, the suction line after the heat exchanger could approach the saturation temperature of the suction gas. If this occurs the suction gas can begin to condense.

    When the compressor again loads up the liquid flies back to the compressor.

    This would require special precautions with the installation to ensure the suction line is not trapped in any manner.

    Look forward to hearing comments of others on this device.

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: variable expansion valve

    With zero superheat, you will never fall within the specs of the compressor manufacturer.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: variable expansion valve

    Yes, maybe zero superheat at the evaporator but is the larger diameter pipe section supposed to be something like an accumulator? Or is it just the scale of the drawing?

    There must be some superheat effect otherwise there wouldn't be any vapour returning ??
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: variable expansion valve

    I don't understand the drawing. If the flow control rod is experiencing colder temperatures... in other words if the liquid is exposed to suction temperatures, such as in a heat exchanger, I would expect it to INCREASE the flow through the orifice as it reduces in size. This is opposite of what is needed. Anyone have any theories on what the flow control rod is doing?

  6. #6
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: variable expansion valve

    This sounds like US Patent # 7611911 which says
    The invention provides for the control of an expansion valve without relying on measuring temperature at the suction side of a compressor. In particular, the control of the expansion valve is premised on a computation of discharge superheat using a mathematical algorithm based upon the current capacity of one or more activated compressors. The computation of the discharge superheat is preferably based on sensed suction and discharge pressures for the one or more compressors. The computed discharge superheat is compared with an actual discharge superheat that is based on a sensed discharge gas temperature. The comparison preferably permits the actual discharge superheat to be within a prescribed amount of the computed discharge superheat. This computational process has a much lower likelihood of error when contrasted with a computation based on sensing suction temperature. In this regard, when the compressor or compressors operate in the so called "flooded condition" (no suction superheat), the measurement of conditions of the refrigerant in an evaporator leaving section or compressor entering section gives no idea about the refrigerant quality (quantity of liquid refrigerant in a mixture) entering the compressor. In reality, when the refrigerant entering the compressor is a saturated gas or mixture of the saturated gas and liquid, the refrigerant temperature is equal to refrigerant saturated temperature with suction superheat being equal to 0. It is impossible to make a distinction between acceptable, transient operation with some liquid droplets entering the compressor and an operation with large amount of liquid, which results in a very rapid compressor failure.

    Computing superheat based on the conditions of the refrigerant at discharge from the compressor allows a control to clearly distinguish refrigerant quality (amount of liquid in a mixture) entering the compressor. Knowing the refrigerant quality while operating with minimal or no suction gas superheat allows for an appropriate control of the EXV opening in a transient, low suction superheat.

  7. #7
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: variable expansion valve

    I got the description for it:

    The variable expansion valve is a patented device (US patents 5,819,548 and 5,913,891) which can provide zero-superheat operation of an evaporator with potentially less cost than a thermostatic expansion valve. The valve and its principle of operation are illustrated in Figure (attached in above post).
    Two concentric tubes and a rod form a liquid-suction heat exchanger at the inlet and exit of an evaporator. The warm liquid travels down the inner tube, around the outside of the rod. The refrigerant exiting the vaporator passes between the concentric tubes. The rod is made
    of a material with a low coefficient of thermal expansion, and the tubes are made of a material with a high coefficient of thermal expansion, preferably aluminum. The evaporator end of the rod pushes up against a flow control orifice. As the liquid fraction exiting the vaporator
    increases, the tubes are cooled, thus causing them to contract, resulting in more throttling at the orifice. When the liquid fraction decreases, the opposite occurs. In this way, the variable expansion valve can maintain evaporator operation with zero superheat. The interchange heat transfer provided by the tube assembly assures evaporation of refrigerant to maximize system
    efficiency and protect the compressors from liquid slugging.

    Hope it's clear.

    rgds
    LC
    I hear...I forget;I see...I remember;I do...I understand

  8. #8
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: variable expansion valve

    As the liquid fraction exiting the vaporator
    increases, the tubes are cooled, thus causing them to contract, resulting in more throttling at the orifice. When the liquid fraction decreases, the opposite occurs. In this way, the variable expansion valve can maintain evaporator operation with zero superheat. The interchange heat transfer provided by the tube assembly assures evaporation of refrigerant to maximize system
    efficiency and protect the compressors from liquid slugging.
    Lc_shi, If I understand you, the rod is the constant and the tubing is the variable? Thus reducing length and causing the rod to throttle because it does not change it's length proportionately?

    The evaporator end of the rod pushes up against a flow control orifice. As the liquid fraction exiting the vaporator
    I picture the rod anchored at the top to the liquid line, permitting flow around it. I then perceive that the rod is not pushing against the flow control orifice, but more likely the orifice is pushing against the rod as the liquid line is contracting toward the rod as a result of the suction superheat reducing.

    Is my understanding consistent with your thinking?

  9. #9
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: variable expansion valve

    I have to add that if I picture this correctly, we do indeed have a thermostatic expansion valve that looks simple in design and inexpensive to manufacture. But oh, what research and devolopment would be necessary to mass produce. It has a theory I can picture working. I am dubious of the practicality. Metallurgy comes to mind. Reaction speed becomes an important consideration. Hysteresis (over and underfeeding under variable load conditions, just in case I used the wrong word) effects will require incredible fine-tuning. Parabolic valve seating would assist, etc.

    To justify what I see as the expense of developing this device, I picture mass produced refrigeration cases or air-conditioners or automobile air-conditioners. All of which have different solutions for changing load conditions. How well it competes with electronic expansion devices, capillary tubing and fixed orifices will be the test of this design.

    On the other hand, if I entirely misundertood your explanation, never mind what I just said. But it still beats the heck out of US Patent # 7611911

  10. #10
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: variable expansion valve

    Dear LC,

    To be honest I have never heard about variable expansion valve. However I agree with Peter 1 that with zero superheat, what would be the characteristic of the compressor. Could you please provide further details on it.

Similar Threads

  1. Fitting an expansion valve question
    By Larry2 in forum Air Conditioning
    Replies: 20
    Last Post: 08-04-2008, 04:17 PM
  2. expansion valve aint cold
    By justinworne in forum Trouble Shooting
    Replies: 6
    Last Post: 26-07-2006, 10:52 PM
  3. Replies: 2
    Last Post: 07-09-2005, 03:07 PM
  4. pressure drop between expansion valve and distributor
    By aygul in forum Technical Speculations
    Replies: 10
    Last Post: 22-01-2004, 09:47 AM
  5. Oversizing EXV electronic expansion valve
    By aygul in forum Technical Discussions
    Replies: 5
    Last Post: 20-11-2003, 01:00 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •