    Post How to determine the size of two-way on/off actuator valve for FCU



    I am new the HVAC.

    I wanted to estimate the size of two-way on/off actuator valve For FCU.

    I have purchased 42CE002,42CE003,42CE004,42CE005 and 42CE006 FCU of carrier make.
    I have attached the data sheet of the same
    I request you to help me with a spreadsheet or any document by which i can select the appropriate size of valve.

    I want to select be limo brand according to tender.

    More over if possible, please give me the link or pdf which explains all the connections to the FCU and their functions,
    for eg what other valves and other apparatus i have to attach to each FCU for its functioning. FCU DATA SHEET.png



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: How to determine the size of two-way on/off actuator valve for FCU

    The links etc should be included with FCU installation manual.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jul 2013
    Location
    INDIA
    Age
    37
    Posts
    5
    Rep Power
    0

    Re: How to determine the size of two-way on/off actuator valve for FCU

    I did not get the installation manual with the units, more over i tried to Google the same out, but i could not find the same, if you can just give me normal line diagram of installation for any FCU, it would help me.

    More over please help me with finding the valve size for each FCU, depending upon its capacity.

  4. #4
    Join Date
    Sep 2014
    Location
    United Stats
    Age
    32
    Posts
    1
    Rep Power
    0

    Re: How to determine the size of two-way on/off actuator valve for FCU

    i will follow this manual to find size of two-way on/off actuator valve for FCU

  5. #5
    Join Date
    Jul 2013
    Location
    INDIA
    Age
    37
    Posts
    5
    Rep Power
    0

    Re: How to determine the size of two-way on/off actuator valve for FCU

    Dear John,
    Which manual you are talking of?

    If you have any link or so,please share the same.

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: How to determine the size of two-way on/off actuator valve for FCU

    Generally the valve will be sized to match the coil connection size, I.e. 1/2" (15mm), 3/4" (22mm).

    The wiring diagram will depend on the control package that you ordered, I think.

    (Edit)

    Try the HDB or NTC controls documents from here....
    http://eto.carrier.com/lit.asp
    Last edited by Brian_UK; 22-09-2014 at 10:34 PM.