    chiller on/off temps



    Hi, I'm working on a brine chiller at a winery, the the setpoint is at -3c. Its a tube evap the brine in is at -2.5c brine out at 0.7 c. Ive not worked on these before. I would have thought the brine out should be at a lower temp, I tried swapping the sensers with the same result. Any advice please?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: chiller on/off temps

    It looks like your evaporator isn't working if the brine temperature is going up not down.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: chiller on/off temps

    has the brine circulating pump been replaced? is it's direction correct? any hero sparkys reversed phase on the pump?

  4. #4
    Join Date
    Sep 2014
    Location
    Australia
    Posts
    12
    Rep Power
    0

    Re: chiller on/off temps

    I confirmed the correct dierction by seeing the brine enter the holding tank. Also check the the system is bringing the brine down to temp ok. After trying head transfer paste as it had none on it, I still couldn't get the brine out temp readout, (b1 on the carel i33) to what it actually was. I decided to leave it as the compressors were cycling off b1brine into the evap anyway, so the b2 didn't appear to affect the performance. Thanks guys.

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: chiller on/off temps

    Hi WCE Bloke.
    Welcome to the forum.
    I suspect you have answered your own question here!
    If the chiller is controlling on Water on the chiller (RWT) then what you are getting is correct.
    Can you advise what chiller it is?
    Or at least what make and model the controller is?
    Also can you swap control to water off (LWT)
    Also have a look at the chilled water circuit strainers, a reduced flow through the evap would exasperate the situation.
    Good luck.
    Having re-read your original post then I would check out the KPA across the evap because it sounds like a potential flow issue?
    Grizzly