  1. #1
    Join Date
    Sep 2014
    Location
    EGYPT
    Posts
    13
    Rep Power
    0

    Smile Thermo king T600 truck unit problem



    Thank you at advance for all of you.I have abig problem at mentioned unit.The unit was installed after storing 4 years.I think It was installed well.I tried to start the unit at diesel engine option .Although the unit is sleep,I found two alarms at SR-2 controller.the first is :high discharge pressure.The second alarm:the diesel engine at low speed.I pushed Clear bottom to cancell alarms but no clearing and consequently no starting for the unit.Please inform me what can I do?Thanks



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Thermo king T600 truck unit problem

    You need to see two zeros to make sure the alarms are clear,if you press select which is the button with the ring of arrows then the equals button to show the zero,s then it should restart.

  3. #3
    Join Date
    Nov 2009
    Location
    Canada
    Posts
    123
    Rep Power
    15

    Re: Thermo king T600 truck unit problem

    Quote Originally Posted by cadwaladr View Post
    You need to see two zeros to make sure the alarms are clear,if you press select which is the button with the ring of arrows then the equals button to show the zero,s then it should restart.
    Its a SR2 Controller Cad, not U-PT

  4. #4
    Join Date
    Nov 2009
    Location
    Canada
    Posts
    123
    Rep Power
    15

    Re: Thermo king T600 truck unit problem

    is thee ***** in the system?

  5. #5
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Thermo king T600 truck unit problem

    Whoops still on you tube tho just needs to put the right search in,could be gas but high head with no gas?

  6. #6
    Join Date
    Nov 2009
    Location
    Canada
    Posts
    123
    Rep Power
    15

    Re: Thermo king T600 truck unit problem

    I cant rember the wiring on the t series but I had a ts 200 hp and lp in same cicuit

  7. #7
    Join Date
    Aug 2011
    Location
    Canada
    Posts
    160
    Rep Power
    15

    Re: Thermo king T600 truck unit problem

    Quote Originally Posted by moggy66 View Post
    I cant rember the wiring on the t series but I had a ts 200 hp and lp in same cicuit
    The TS series (upT controller) has a low and high pressure switch in series, the T series (SR2/3) should have transducers if it has an etv and seperate pressure switches if not.

  8. #8
    Join Date
    Sep 2014
    Location
    EGYPT
    Posts
    13
    Rep Power
    0

    Re: Thermo king T600 truck unit problem

    Today ,I diconnected the wires for high pressures but withiut any result.I expected to see alarm for high pressue cut out but it was the same fault alarm high pressure discharge.By the way the unit has *****.I phoned thermo king agent in Egypt who told me that the software needs to be reloaded.I tried seveal times to clear alarms but no clearing.

  9. #9
    Join Date
    Nov 2009
    Location
    Canada
    Posts
    123
    Rep Power
    15

    Re: Thermo king T600 truck unit problem

    Quote Originally Posted by IRMechanik View Post
    The TS series (upT controller) has a low and high pressure switch in series, the T series (SR2/3) should have transducers if it has an etv and seperate pressure switches if not.

    Thx Paul......

  10. #10
    Join Date
    Aug 2011
    Location
    Canada
    Posts
    160
    Rep Power
    15

    Re: Thermo king T600 truck unit problem

    Quote Originally Posted by sanad View Post
    Today ,I diconnected the wires for high pressures but withiut any result.I expected to see alarm for high pressue cut out but it was the same fault alarm high pressure discharge.By the way the unit has *****.I phoned thermo king agent in Egypt who told me that the software needs to be reloaded.I tried seveal times to clear alarms but no clearing.
    Does the unit have a standard or premium HMI? with the premium hmi you can get into the gauge menu and see what the transducer is showing. Try jumping the the hpco (it's normally closed switch) I would advise against running the unit with any of the safeties bypassed but with the switch jumped you should be able to clear the code and narrow down your problem.

    Thx Paul......
    NP

  11. #11
    Join Date
    Sep 2014
    Location
    EGYPT
    Posts
    13
    Rep Power
    0

    Re: Thermo king T600 truck unit problem

    Yes I jumped the high pressyr switch but no response.I have 3 alarms now. 1- discharge high pressuire. 2- low speed diesel engine. 3- restart nul.

  12. #12
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    349
    Rep Power
    18

    Re: Thermo king T600 truck unit problem

    is the battery charged ?
    High discharge pressure can be deceiving as it can also indicate a run relay circuit error. Code 35.
    check all safety switches.
    If the engine low speed alarm comes on without it running check the oil pressure switch. disconnect it and see what happens.

  13. #13
    Join Date
    Jun 2014
    Location
    yunlin
    Age
    38
    Posts
    24
    Rep Power
    0

    Re: Thermo king T600 truck unit problem

    how much ***** presure?
    did you ever try the micro pin?
    OR short the wire of discharge presure

  14. #14
    Join Date
    Aug 2011
    Location
    Canada
    Posts
    160
    Rep Power
    15

    Re: Thermo king T600 truck unit problem

    Quote Originally Posted by sanad View Post
    Yes I jumped the high pressyr switch but no response.I have 3 alarms now. 1- discharge high pressuire. 2- low speed diesel engine. 3- restart nul.
    Restart null code will usually follow code 10 (high discharge pressure) basically mean the unit is going to wait and try and restart later.

    Check F25 (7.5a) power to high pressure cutout. Also powers the fuel pump and fuel solenoid.

  15. #15
    Join Date
    Sep 2014
    Location
    EGYPT
    Posts
    13
    Rep Power
    0

    Re: Thermo king T600 truck unit problem

    Yes ,engineering manager at the thermoking agent had told me the same.He said if the fuel pump is runnig,the alarm of high pressure discharge will be cleared and restart null will follow it.I will come back to you after trial.

  16. #16
    Join Date
    Sep 2014
    Location
    EGYPT
    Posts
    13
    Rep Power
    0

    Re: Thermo king T600 truck unit problem

    Hi,IRMechanik
    Thank you very much .I found F25 open.So,Ireplaced it.The unit is running well electrically and Diesel.Alarm of high pressure discharge disappeared.

  17. #17
    Join Date
    Sep 2014
    Location
    EGYPT
    Posts
    13
    Rep Power
    0

    Re: Thermo king T600 truck unit problem

    My freinds
    the diesel engine is going to start but no fuel.Ifound the fuel pump does not work where the coil is burned.I checked the coming power to the pump but nothing.I am going to replace the fuel pump but how to what about the the lost power.
    awaiting yr reply.

  18. #18
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    349
    Rep Power
    18

    Re: Thermo king T600 truck unit problem

    would it not be F25 open again Sanad ?

  19. #19
    Join Date
    Sep 2014
    Location
    EGYPT
    Posts
    13
    Rep Power
    0

    Re: Thermo king T600 truck unit problem

    Fuse F25 is ok.When I installed the new fuel pump ,It is running well now.Thank you very much.

  20. #20
    Join Date
    Aug 2010
    Location
    izmir
    Posts
    38
    Rep Power
    0

    Re: Thermo king T600 truck unit problem

    Please follow this ling

  21. #21
    Join Date
    Aug 2010
    Location
    izmir
    Posts
    38
    Rep Power
    0

    Re: Thermo king T600 truck unit problem

    vercion 1
    https://www.youtube.com/watch?v=wMvwdNM7zvU

    vercion 2 blockbox 02 model

    https://www.youtube.com/watch?v=pn3_MPfFDew

    In the same characteristics as the original

  22. #22
    Join Date
    Oct 2014
    Location
    Australia
    Posts
    37
    Rep Power
    0

    Re: Thermo king T600 truck unit problem

    Any more dramas I would do a cold start.
    Have had lots of strange codes on SR2 & 3 truck units.
    Definitely changing a lot more controller / boards these days