    high sub cool,high super-heat with r410A



    Dears,
    Today I checked RHEEM 3.5 ton SAGL split unit. The complaint was ice forming frequently on cooling coil. As per my primary checking suction superheat is high 33K and sub cooling is 14k. Liquid line filter is ok and the metering device is TXV factory adjusted. The refrigerant 410a, the contractor used brand FREO + unknown brand refrigerant. I think china. Before doing any action, I felt may be the refrigerant is mixing and contaminated. Now the evacuation is in progress……
    after charging the with good refrigerant ,let us see the readings.Am I correct?
    Last edited by moideen; 14-09-2014 at 10:16 AM. Reason: ref.name changed 410a



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: high sub cool,high super-heat with r410A

    Hi Moideen
    Changing the refrigerant for fresh and to the correct charge is a good first step as this will allow you to disregard these as a possible problem with further trouble shooting on the system

  3. #3
    Join Date
    Feb 2011
    Location
    Russia
    Posts
    26
    Rep Power
    0

    Re: high sub cool,high super-heat with r410A

    Massflow of refrigerant is too low. Maybe expansion valve is almost closed. Try to heat thermo bulb.

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: high sub cool,high super-heat with r410A

    Also no suction or discharge pressure readings to relate to anything.
    You may have them but we do not.
    IF you new nothing of previous work, would you have done the same thing!

  5. #5
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: high sub cool,high super-heat with r410A

    already evacuation started, i will update all new readings....

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: high sub cool,high super-heat with r410A

    There have been problems with txv's failing due to a chemical reaction of some rust proofing chemical copeland started using and the systems refrigerant and oil making a sticky substance which gums up the orifice. It gives symptoms of a failed txv.

    http://www.danfoss.com/North_America...0408F9223.html