    Condenser approach temp



    The trane RTWD condenser was cleaned. The approach temp. before was 25°F and now it's 14°F still high. I am suspecting about the volume of water entering the condenser. Is there any instruments to measure the amount of water entering?. I saw that the scales in the tubes were removed. Pls...help

    Thank you...



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Condenser approach temp

    You need ultrasonic flow meter for that purpose.

  3. #3
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: Condenser approach temp

    overcharged system may indicate higher condenser approach.

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Condenser approach temp

    Quote Originally Posted by roelescence View Post
    The trane RTWD condenser was cleaned. The approach temp. before was 25°F and now it's 14°F still high. I am suspecting about the volume of water entering the condenser. Is there any instruments to measure the amount of water entering?. I saw that the scales in the tubes were removed. Pls...help

    Thank you...
    Did you look down or blow through each tube to make sure they are not blocked.
    Chemical clean not always perfect if blocked in middle of tubes.
    Have you checked water strainers, sump water level & pump operation.

    Are there any valves, etc in water lines that could restrict flow.
    Also water sprays in cooling tower.

  5. #5
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Condenser approach temp

    Is the water flow in the condenser the correct way around ?

  6. #6
    Join Date
    Mar 2012
    Location
    italy
    Age
    67
    Posts
    78
    Rep Power
    13

    Re: Condenser approach temp

    Use a differential pressure gauge to measure the pressure loss.
    check the correct pressure drop from the manufacturer's manual.

  7. #7
    Join Date
    Sep 2014
    Location
    philippines
    Posts
    20
    Rep Power
    0

    Re: Condenser approach temp

    There are gate valves and check valves in the water line. Gate valves are old but we've just replaced the check valves

  8. #8
    Join Date
    Sep 2014
    Location
    philippines
    Posts
    20
    Rep Power
    0

    Re: Condenser approach temp

    There are check valves in the water line, and flow cannot be reversed

  9. #9
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: Condenser approach temp

    what is the inlet and outlet temp of condenser?

  10. #10
    Join Date
    Sep 2014
    Location
    philippines
    Posts
    20
    Rep Power
    0

    Re: Condenser approach temp

    Condenser inlet is 84.2°F and out is 92.1°F.
    By the way pls analize this reading for the compressors:
    L1 92.5%
    L2 93.5%
    L3 100.3% of its rated current. Isnt it imballanced?

  11. #11
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: Condenser approach temp

    As per your condenser delta T (8F) the chilled water flow is ok. But your inlet water temperature is high considering local ambient wet bulb temperature. I think your wet bulb is 70F (google).then condenser inlet should be 75F.arount 9f is high. Check your cooling tower whether it is performs. When inlet temperature is high, approach also will be high.