    Pipe sizing question



    Hi,
    I have limited information but maybe someone can point me in the right direction
    I am installing 2 Vogt Ice machines 25,000 lbs of ice per day per system.
    The refrigerant is NH3
    The Two machines will share a common surge drum but I have questions
    Can I have one wet suction header connecting the two in parallel?
    Or should each machine have its own wet suction back up to the surge drum?
    My dry suction back to the engine room will be in excess of 500'
    How do you calculate the necessary line size and do I need to reduce the line as it travels out to the surge drum?



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Pipe sizing question

    TF12 if you go to vogt ice website, download appropriate ice machine manual & if advises sizes & how to pipe up system.

  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Pipe sizing question

    http://www.vogtice.com/wordpress/wp-...ice-Manual.pdf
    http://www.vogtice.com/wordpress/wp-content/uploads/P24A-and-P34A-Manual.pdfhttp://www.vogtice.com/wordpress/wp-content/uploads/P24AL-P34-AL-Manual-.pdf

    3.17 & 3.18 in P24AL-P34AL manual give piping example.
    Assuming you would have P18AL machines.

    Guessing each ice machine suction 2" & main line back to slop pot 3 to 4 "
    Each ice machine has to have a suction solenoid/ evaporator pressure regulator for them to harvest individually
    & not allow suction pressure to get to low in each ice machine.
    Last edited by RANGER1; 13-09-2014 at 10:54 AM.