    Bit of an oddity



    I've put in a A2W 4 ton HP (R410A) and I just wanted to confirm a couple things.
    I'm getting the unit cutting out after about 5-6 min of operation, 5 min delay and back on again. Setpoint on the tank is not satisfied and outdoor temp is close to 14C
    The most stable I can get for readings is:

    98 psi suction and 136 discharge
    4C SH and -6 SC
    liquid side of the hx is 33 out and 29 in

    I think she is overcharged a bit but cannot figure out why she is cutting out. Head pressure never gets anywhere near critical and she is liquid injected as well (but it never gets to the point of needing it)

    Any thought?

    I'm in the north of Newfoundland and have a flight booked in a couple of hours to get back to Toronto so I have to resolve at least the fridge side, hoping the rest is electrical (programming)



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Bit of an oddity

    Where are you measuring high pressure, can you get a tap on the discharge line to verify pressure is ok?
    Mostly found in the southern part of this green and pleasant land.

  3. #3
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Bit of an oddity

    I'm gone now and back in Toronto. The only place I could make any measurements is at the service valves. Pot temp did show at around 90C, the unit is tied into the manufacturer now by the interweb so they can see some of the issues. Not all, though.

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Bit of an oddity

    Service valves may not give true discharge, especially if it is a split type outdoor, water flows alright?
    Mostly found in the southern part of this green and pleasant land.

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Bit of an oddity

    still waiting for a model number and manufacturer -to see if i can find a manual

  6. #6
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Bit of an oddity

    Quote Originally Posted by install monkey View Post
    still waiting for a model number and manufacturer -to see if i can find a manual
    haha. No manuals worth anything for this model. Not in the same league as Mitsi or Fujitsu.

    Google Ecologix
    Last edited by MikeHolm; 14-09-2014 at 01:12 AM.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Bit of an oddity

    Quote Originally Posted by MikeHolm View Post

    98 psi suction and 136 discharge
    4C SH and -6 SC
    liquid side of the hx is 33 out and 29 in
    These pressures and temperatures marked red does not have sense to me.
    Where did you take that "discharge" pressure
    Also, how did you calculated that negative subcooling temperature?

    Give us all readings and where on system did you took them.

    Also, you said that unit is "cutting out", but you did not say at what alarm (high pressure, low pressure, high discharge temperature, etc....) it is happening.

    136-98=38 PSI
    looks to me like pressure drop at evaporator (outdoor unit if it is split type) and belonging piping and maybe some kink on these pipes.
    Last edited by nike123; 14-09-2014 at 07:27 AM.

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Bit of an oddity

    http://www.ecologix.ca/wp-content/up...-Heat-Pump.pdf
    install manual- love the hand sketched wiring diagram

  9. #9
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Bit of an oddity

    Quote Originally Posted by install monkey View Post
    http://www.ecologix.ca/wp-content/up...-Heat-Pump.pdf
    install manual- love the hand sketched wiring diagram
    This is a A2W, totally different beast with liquid injection.

  10. #10
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Bit of an oddity

    Quote Originally Posted by nike123 View Post
    These pressures and temperatures marked red does not have sense to me.
    Where did you take that "discharge" pressure
    Also, how did you calculated that negative subcooling temperature?

    Give us all readings and where on system did you took them.

    Also, you said that unit is "cutting out", but you did not say at what alarm (high pressure, low pressure, high discharge temperature, etc....) it is happening.

    136-98=38 PSI
    looks to me like pressure drop at evaporator (outdoor unit if it is split type) and belonging piping and maybe some kink on these pipes.
    The pressure readings were taken at the service valves and the temps were 4-5cm closer to the comp but I couldn't get much closer to the comp. The Digicool gives SC readings in -C if the temp reading is higher than the high side bubble point, although the temps shown at that time were 0.8C and 8C so I'm not sure why it displayed the negative. Evap is just coil and TXV. and I'm quite sure there is no bad kink in the 7/8" or 1/2" lines.

    There is quite a bit of monitoring on this unit (despite the crappy manual) and it has never given an error reading of any type. It just cuts out.

    The manufacturer can get some readings via the net but I'm not sure what they can do.
    Last edited by MikeHolm; 14-09-2014 at 12:51 PM.

  11. #11
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Bit of an oddity

    136psi discharge!!- on r10a - pot goosed!

  12. #12
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Bit of an oddity

    Oh, I hope not, this is where it is. It had a 60psi differential when running most of the time but the last run was only 10psi.

    https://www.google.ca/maps/place/L%27Anse+aux+Meadows,+NL+A0K/@50.2445036,-57.0434481,5z/data=!4m2!3m1!1s0x4b83fe0a482d8213:0x7da6bd7dfe25d101?hl=en
    Last edited by MikeHolm; 14-09-2014 at 03:10 PM.

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Bit of an oddity

    Is that unit with 3 phase scroll compressor?

  14. #14
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Bit of an oddity

    @mike

    liquid side of the hx is 33 out and 29 in
    If you have 29°C entering and 33°C temperature of water leaving heat exchanger, which is in this case condenser, than you certainly cannot have discharge pressure of 136 PSIG (8.5°C dew point temperature for R410A). One of these two measurements is not correct.
    By the laws of physics, discharge pressure at compressor must be at least above saturation temperature of 33°C (281 PSIG).
    Last edited by nike123; 14-09-2014 at 07:59 PM.

  15. #15
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Bit of an oddity

    This pot has never got higher than perhaps 180psi discharge (measured at the service valves) and at that time condenser leaving temp was 43C and intake was 40C. Those liquid temps were measured by the unit controller.

    Does this look at all like a gross over charge?

  16. #16
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Bit of an oddity

    Mike, I still cannot see how discharge pressure could be that low with such condenser water temperatures.
    To me, it looks like something is not right with these measurements.

  17. #17
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Bit of an oddity

    I will have to get the owner to get a set gauges and temp probes and make some measurements. For me it would be a 3 hr flight and 3 hr drive to the property.

  18. #18
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Bit of an oddity

    Since that is probably inverter compressor, all readings should be taken in TEST mode.
    What is operational range (highest outdoor air temperature) for that unit?

  19. #19
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Bit of an oddity

    It is a 2 stage comp, Copeland ZPS60k4E (or maybe 5E, cannot remember). It started off running around 23A and at worst went up to 33A. Definitely not right.

    Highest outdoor it should see is 30C and lowest is -40C but it will be off at that point and there is a backup electric boiler.

  20. #20
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Bit of an oddity

    My two cents (or whatever the euro is worth these days)

    Get line tap on discharge or tee off HP switch
    disconnect back up heater in case it's acting the maggot

    take pressures temps then, does sound like compressor is knackered but maybe if you find cause of HP trips you can salvage it
    Last edited by al; 15-09-2014 at 09:10 PM. Reason: got distracted by 50 ways to kill your mammy
    Mostly found in the southern part of this green and pleasant land.

  21. #21
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Bit of an oddity

    If the manufacturer pays for a trip to do the work, I'd be happy to go but it will be $2000 just to get there and back.

    Al, the backup isn't tied in to the HP as yet, no matter what yo mammy says (so no need to kill her)

  22. #22
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Bit of an oddity

    Making an educated guess.

    either expansion device is totally open (is EEV or TEV)
    or
    the compressor internal relief valve is passing

  23. #23
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Bit of an oddity

    ya sounding like the pot is tripping on the clixon over load protector, the cycling times seems to jive with that
    Now in Redvers Sask.