    Cold Room Design



    Dear All,

    We have recently designed a cold room system in order to maintain Temperature = 4 - 6°C and Relative Humidity = 50 ± 5%.

    We are achieving the conditions during most part of the day however we have problems during following situations:

    1. DEFROST CYCLE:
    During the defrost cycle the Rh is shooting upto 70% Rh which is not acceptable.

    Defrost cycle is set for 3 minutes every hour.

    2. COMPRESSOR CUT OUT:

    During compressor cut off which is set at 4°C again the Rh is shooting upto 70%.

    The above increase in relative humidity is not acceptable to the client even though the increase is only for 5 to 8 minutes in a hour.

    Please give us your valuable suggestions regarding how to short out the problem.

    Regards

    vijay_study@rediffmail.com


    Vijay Kumar
    HVAC Design Engineer

    BMCPL

    "The more you sweat in peace less you bleed in war"

  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Cold Room Design

    Compressor must never stop, and correction of temperature to be done via electric heaters of the same capacity, and controlled with triacs.

    Defrost must be prevented by using a saturation sensor, which will bypass hot gas when evap temp is below the frost point

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Cold Room Design

    A temperature change from 4 to 6°C with the same absolute humidity gives already a 6%RH change.
    This phenomena is the result of a nature law which you can't change at all.

    So the first thing you have to take care of is to control your temperature much narrower.

    Finetune afterward the RH with electrical heaters, preferable controlled with a PID algorithm.

    If you don't want a change at all, you only can achieve this with a proportional control of cooling and heating.

    Is it a DX evaporator or a water coil?

    What's the product in the room?

    Is it often opened?

    Why you need anyhow a defrost with a temperature of 4 to 6°C, especially with these low RH?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Cold Room Design

    This seems like the evaporating temperature was selected well below 0C to provide dehumidification in an attempt to reach 50% RH.

    When you start to approach evaporating temperatures below 0C for environmental chambers (this is what you are trying to accomplish, this is not a normal cold room situation) you can have these problems.

    The system must never be shut down, or if it is, then you need redundant refrigeration systems.

    You may have to treat the problem as multiple systems.

    1. The refrigeration systems provides the low temperature.

    2. Reheat controls the discharge air temperature to the tolerance you need.

    3. Humidity injection or desiccant systems may be required to fine tune the air condition.

    The temperature of the evaporator coil must operate above the air dew point temperature or frost will form.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Cold Room Design

    I also wonder where the temperature and humidity sensors are located in relation to the cooling coil.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Cold Room Design

    Hi Vijay

    the only way I can think of acheiving constant RH is to fit two evaporators, run one defrost one, then run the other.

    Kind Regards. Andy

  7. #7
    Join Date
    Mar 2006
    Location
    maharashtra
    Posts
    9
    Rep Power
    0

    Re: Cold Room Design

    Quote Originally Posted by vijay_study View Post
    Dear All,

    We have recently designed a cold room system in order to maintain Temperature = 4 - 6°C and Relative Humidity = 50 ± 5%.

    We are achieving the conditions during most part of the day however we have problems during following situations:

    1. DEFROST CYCLE:
    During the defrost cycle the Rh is shooting upto 70% Rh which is not acceptable.

    Defrost cycle is set for 3 minutes every hour.

    2. COMPRESSOR CUT OUT:

    During compressor cut off which is set at 4°C again the Rh is shooting upto 70%.

    The above increase in relative humidity is not acceptable to the client even though the increase is only for 5 to 8 minutes in a hour.

    Please give us your valuable suggestions regarding how to short out the problem.

    Regards

    vijay_study@rediffmail.com
    dear vijay

    In my view you should put off evaporator fans during defrost and compressor off cycle. this may help to avoid excess rh
    sunil bhat
    sunilbhat1@hotmail.com

  8. #8
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Cold Room Design

    had this before, think the guys are telling you your kits not up to it,if its a single evap/condenser every time the compressor stops for whatever reason the RH wil shoot up,in fact at night when the unit is left shut and unatended the off cycle is often a lot longer and then the RH goes through the roof, you could try shortening the cut in /out diff as close as you can , use off cycle defrost [just the fans no heaters], put a good size dehumidifier in the room[plasteres rental size], if it works install a perminent one, theese are only quick fixes to prove a point, as previousley stated, big upgrade needed.

  9. #9
    olumide's Avatar
    olumide Guest

    Re: Cold Room Design

    Hello everybody,
    I am highlly intressted in cold room designing,but am about sitting for my NVQ2 examination by june as Refrigeration and Air-condition engineer,I will be glad if anbody can help to achivied my dream.
    Last edited by olumide; 09-01-2007 at 01:04 PM.

  10. #10
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Cold Room Design

    The thread is an old one, but as I viewed it now, I thought that may be I could suggest something in case the problem is still persisting.

    The Room Temp. is 4 to 6 Deg. C with a RH of 50 %. Firstly, the evaporator should have a air defrost system. The Fan should run. Defrosting every hour for 3 mnts is not required. In such case the defrost would be for 5 to 10 mnts every 6 hours.

    What was the product loaded and what about the door service. What is the coil details such as fins per inch, air flow etc. Are these coils locally fabricated or are of standard manufacture.

  11. #11
    Join Date
    Jun 2007
    Location
    india
    Age
    55
    Posts
    6
    Rep Power
    0

    Re: Cold Room Design

    Hi,

    B4 getting into the probs, first let me be explained why do you need a defrost for such a positive temp

  12. #12
    Join Date
    Jun 2007
    Location
    india
    Age
    55
    Posts
    6
    Rep Power
    0

    Re: Cold Room Design

    vijay, giv more details about the product u r storing. lets know if all the fundas are right

Similar Threads

  1. Cold Room Design - minus 25deg C
    By vijay_study in forum Fundamentals
    Replies: 34
    Last Post: 11-11-2009, 07:12 AM
  2. Cheese Room Design 24V DC
    By jbelding in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2006, 03:23 PM
  3. Installation of cold room
    By Josip in forum Legal-Business-Marketing
    Replies: 12
    Last Post: 12-03-2006, 09:20 PM
  4. Cold Storage Design
    By abbasi in forum Technical Discussions
    Replies: 11
    Last Post: 06-01-2005, 07:17 PM
  5. Large cold room for fresh produce made of Glass
    By allanbaker in forum New Technologies
    Replies: 3
    Last Post: 11-05-2004, 09:04 PM