    help with brema ice maker



    hi, i have a brema ice maker cb 30 model, r404a, water cooled condensor,
    tripping out on head pressure @30bar. removed gas and weighed back in factory charge,thing is works ok while im there and an hour later trips out,at start of cycle head pressure goes as far as 26 bar and drops as the cycle goes on,water regulator valve is fully open and water supply seems ok,any ideas appreciated,thanks.



  2. #2
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: help with brema ice maker

    Whats the water quality like? Scale likes to build up on the hot spots of heat exchangers, how smoothly is the water valve moving. Once you know the hx and valve are opperating correctly then we can look into the rest of the system, sticky lls weak hp switch so on.
    Now in Redvers Sask.

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: help with brema ice maker

    any strainers on the water circuit?

  4. #4
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: help with brema ice maker

    Is this a new system ?
    What type of condenser is it ie Shell & Tube,Plate ?
    Which way does the water flow through the condenser, in the bottom out the top , in the top out the bottom ?

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: help with brema ice maker

    Faulty water regulator valve, maybe. Or water supply intermittent cut offs.
    Are you sure in your correct model name?

  6. #6
    Join Date
    Mar 2012
    Location
    italy
    Age
    67
    Posts
    78
    Rep Power
    13

    Re: help with brema ice maker

    Exchanger with low heat transfer due to dirt.
    low flow of cooling water.