    Welcome to the unknown...



    Okay so I'm on a site with a colleague of mine and we came across an Airedale DF60X2-EZ that has been intermittently tripping mcb 10.

    We have replaced/swapped the following components:
    Hp and lp switches
    Condenser fan motor
    Pco controller
    Transformer
    air flow switch
    On/off module
    both compressor contactors, overloads and aux contactors
    Indoor fan motor
    Both indoor fan motor contactors
    Fan speed controller
    The mcb itself
    we have also megga'ed the clixons for both the compressors and the discharge sensors...

    As you can tell, we are clutching at straws here!

    The cable going into the mcb is from the transformer and feeds the block which supplies the 24v circuit. Everything we have checked is fine...

    Can anyone shed some light?

    Thanks peeps



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Welcome to the unknown...

    What is the type and rating of the MCB?

    What is the maximum operating current of the unit (from the nameplate)?

    Why would you megger the Klixon's on the compressors?

    How did you megger the Discharge Sensors?

    Have you megger'd the compressors?
    Last edited by frank; 09-09-2014 at 02:38 PM. Reason: Added more questions

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Welcome to the unknown...

    So you are saying that mcb10 on the 24volt control circuit, is that correct?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Welcome to the unknown...

    Follow the wire my friend, always follow the wire...
    The truth will be out there.


  5. #5
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Welcome to the unknown...

    Ask your self how does a circuit breaker work, and what is its function, go from there.

    I'll throw a bone: they work on 3 principles, Current, time and temperature they all inter act with each other.

    High current means less time for it to trip, raise the ambient this takes less current or a shorter time for it to trip.

    Under sized wires have voltage drop means for more current as an example

    I all so didn't read of you replacing the circuit breaker! as they can become weak over time.
    Last edited by The MG Pony; 13-09-2014 at 05:34 PM. Reason: added details
    Now in Redvers Sask.

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Welcome to the unknown...


  7. #7
    Join Date
    Jul 2012
    Location
    England
    Posts
    22
    Rep Power
    0

    Re: Welcome to the unknown...

    Quote Originally Posted by The Viking View Post
    Follow the wire my friend, always follow the wire...
    The truth will be out there.

    But which wire Viking ;-)

  8. #8
    Join Date
    Feb 2014
    Location
    london
    Age
    38
    Posts
    24
    Rep Power
    0

    Re: Welcome to the unknown...

    Disconnect components (loads) each a time and see if the Mcb will trip until you find it. It works every time,
    No need to check switches like klixon, switches are not loads and they will never trip any mcb. If a switch fails the unit will not run. If anything trips you need to check the loads eg solenoid, compressor, fans, crank case heater, evap heater ..ect
    Also have you megged the compressor?

  9. #9
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Welcome to the unknown...

    from original post
    "The cable going into the mcb is from the transformer and feeds the block which supplies the 24v circuit."
    thus its on the control circuit, it could be "a switch like a klixxon" as they are on the control circuit, they will not pull a load but they are capable of failing



  10. #10
    Join Date
    Feb 2014
    Location
    london
    Age
    38
    Posts
    24
    Rep Power
    0

    Re: Welcome to the unknown...

    So if a switch like klixon fails, the circuit will break and stops the compressor. But why would that cause mcb to trip?

  11. #11
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Welcome to the unknown...

    grounding if its faulty

  12. #12
    Join Date
    Feb 2014
    Location
    london
    Age
    38
    Posts
    24
    Rep Power
    0

    Re: Welcome to the unknown...

    thats true, i remember i had an isolator grounded and tripping the breaker.

  13. #13
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Welcome to the unknown...

    Grounding 24V control circuit cannot trip fuse because transformer is isolated from grounding, therefore, circuit cannot be closed through grounding. Same thing as isolation transformer at your bathroom for shaving machine. Also, that is the reason why it is transformer installed to control circuit.

    It is overloaded by some of the components or wiring is faulty or fuse is of wrong type or wrong size or wrongly dimensioned.

    To OP:

    First check that all wiring is as on wiring diagram.
    Remove ALL components and transformer from control circuit and leave only wiring and terminals, than masure resistance with multimeter, and if it is infinite, meger (100V) wiring between two poles starting from transformer then each branch of control circuit wiring.
    Last edited by nike123; 28-09-2014 at 08:12 PM.

  14. #14
    Join Date
    Feb 2014
    Location
    london
    Age
    38
    Posts
    24
    Rep Power
    0

    Re: Welcome to the unknown...

    Matt, any update on this fault?