    Is it possible to test a Daikin vrv 3 system without control being set up?



    Hi everyone. I have a Daikin tech coming in to do a system start up which will pretty much entail them setting up the Intelligent Touch Manager from what I understand. However, they won't be in for a few days.

    Is it possible to run a test on a Daikin VRV 3 system without the controller set up to and units not addressed? Any help is appreciated.



  2. #2
    Join Date
    Jul 2012
    Location
    England
    Posts
    22
    Rep Power
    0

    Re: Is it possible to test a Daikin vrv 3 system without control being set up?

    It is possible, do your units also have individual remote controls ?

  3. #3
    Join Date
    Oct 2012
    Location
    Russia
    Age
    42
    Posts
    392
    Rep Power
    18

    Re: Is it possible to test a Daikin vrv 3 system without control being set up?

    Without central control or individual control can`t.

  4. #4
    Join Date
    Aug 2014
    Location
    USA
    Posts
    7
    Rep Power
    0

    Re: Is it possible to test a Daikin vrv 3 system without control being set up?

    With no remote controls. I was told by Daikin that it is not possible and had to get a brc controller to start up each system individually, which I did and discovered a bad board-- system still works though, just cant see system status on condensing unit.