    Vacuum test acceptable leak rate



    Does anyone have any documentation about acceptable leak rate when we do vacuum leak test!
    I am unable to find any literature except one precommisioning documentation from my recent job at oil field equipment in Kazahstan.


    In that documentation is stated that after isolation of system from vacuum pump when it is 500 microns has achieved and held for specified time, system pressure should not rise more than 100 microns per hour. Monitoring time should be at least 4 hours after 1 hour of initial monitoring (where pressure should not rise at rate more than 100 microns or else evacuation should be continued). And, end vacum after these 5 hours of monitoring should not rise above 1000 microns.

    I am unable to connect, let say, 0,5g/y of R22 leak with vacuum gage leak rate in microns per hour.

    Here is some literature about that, but I am still unclear how to connect these two numbers.
    http://www.vtechonline.com/pdf/VTech...%20Methods.pdf

    Question is inspired with this video:
    Last edited by nike123; 03-09-2014 at 10:42 PM.



  2. #2
    hookster's Avatar
    hookster is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2007
    Location
    Hampshire
    Posts
    438
    Rep Power
    32

    Re: Vacuum test acceptable leak rate

    You obviously have some serious thinking on the go nike123? Most of us just think leak oh yes, lets fix it!

    There is some excellent information on the institute of refrigeration service engineers section.
    For example the evacuation procedures which is free to service engineer members.

    http://www.ior.org.uk/ior_filter_tec...p?r=34EM3M4NAE


    My attempt is this!
    The refrigerant leakage rate can be calculated in flow rate as per below, then you will need to convert your vacuum leakage to a flow (leaving this to you ) Qleak= Qrefrigerant x Vrefrigerant / Vleak.

    PV=G/MRT

    if G= 0.5grams
    m=86.47 grams/mole R22
    R= Gas Constant 96.15469 J/(kg·K)T= 293K

    answer in litres per year = 162.9 mbar l/year
    Last edited by hookster; 04-09-2014 at 07:36 AM.
    I love the smell of Ammonia in the morning!

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Vacuum test acceptable leak rate

    @hokster

    Thanks for your input!

    It is interesting how nobody else has jet contributed with comments about this topic, and we are suppose to know what we are doing when we do our commissioning jobs.
    I expected lot more inputs about this topic. Or it is very busy week for our top technicians that they have no time for this now?


    OFF topic start:
    Recently, I don't see many new post here on RE.
    OFF topic end.

    Lets continue with subject.

    In literature leak rate for refrigerant is in g/year. But, I ask myself at what conditions (pressure differential between inside of system and outside of system) are given those numbers? Steady pressure at unit standstill, or condensation highest pressure, or evaporation pressures? I expect at corresponding pressures of at least 50°C condensation temperature for given refrigerant (worst case scenario).

    Then, how to convert that to vacuum pressure differential (cca 1 bar) conditions for vacuum leak rate test?

    Any calculation example?