Results 1 to 5 of 5
-
03-09-2014, 05:42 PM #1
Oil charge for commercial compressor
Due to a lack off think , a peer discharge all the oil from the compressor , and did not measure how much it was.
The compressor is a Tecumseh AK526-KS-116 AKM26ES compresor akm526.jpg
Refrigerant is R22 , still is allowed in our country
Thanks in advance
-
03-09-2014, 07:54 PM #2
Re: Oil charge for commercial compressor
Hi
Oil charge is 537ml of 32 grade oil
-
03-09-2014, 08:42 PM #3
Re: Oil charge for commercial compressor
Hi Glenn , thanks for the info .
Could you give me the data font, or where I can find such data for other compressor?
-
04-09-2014, 03:21 PM #4
Re: Oil charge for commercial compressor
it will be an Alkylbenzen oil bty, failing that mineral will work.
Now in Redvers Sask.
-
05-09-2014, 12:23 AM #5