    Exclamation superheat
    can anybody tell what is the normal suction superheat of R134a gas in central air conditioning system..???
    May 2012
    59
    1,528
    Re: superheat
    Normal is very vague
    But if it is working with an expansion valve, most
    valves come pre-set to about 6 - 8 degs of superheat.
    That is measured out of the evaporator. If you measure the
    suction closer to the compressor the superheat will be higher.
    Rob
    Mar 2014
    S.OF.OMAN
    44
    Re: superheat
    6-8 deg f or deg c ... txv is using in this chiller, am measuring suction near compressor..
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    Re: superheat
    Quote Originally Posted by Shajan John View Post
    centigrade.suction superheat
    Re: superheat
    It is degrees Kelvin not C or F.
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    Re: superheat
    Dear brian, please check example in DEG.C.
    Suction line temp = 12C.
    Saturated suction temp = 4c.
    Superheat = 8c.
    In deg.Kelvin also same value .as per my understanding Kelvin is positive value. it is better to use in minus temp to calculate superheat.
    Split Croatia
    6,151
    Re: superheat
    Use in conjunction with Celsius[edit]
    A thermometer calibrated in degrees Celsius (left) and Kelvin (right).
    In science and in engineering, degrees Celsius and kelvins are often used simultaneously in the same article (e.g. "...its measured value was 0.01028 °C with an uncertainty of 60 µK..."). This practice is permissible because the degree Celsius is a special name for the kelvin for use in expressing Celsius temperatures and the magnitude of the degree Celsius is exactly equal to that of the kelvin.[10]Notwithstanding that the official endorsement provided by Resolution 3 of the 13th CGPM states, "a temperature interval may also be expressed in degrees Celsius", the practice of simultaneously using both "°C" and "K" remains widespread throughout the scientific world as the use of SI prefixed forms of the degree Celsius (such as "µ°C" or "microdegrees Celsius") to express a temperature interval has not been widely adopted.[4]
    Wikipedia ........
    May 2012
    59
    1,528
    Re: superheat
    Quote Originally Posted by moideen View Post
    Superheat = 8c.
    You are right up to a point Moideen but what Brian said is correct
    When we explain a difference in temperature we explain it as degrees Kelvin
    that means you are talking about a difference between two temperatures and not
    the temperature in Deg C.
    If the saturation temp is 0 deg C and the suction is 8 deg C then the difference is 8K
    (8 degrees Kelvin).
    To avoid confusion temperature difference is always expressed as Degrees Kelvin.
    Rob
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    Re: superheat
    (8 degrees Kelvin).
    Rob
    absolutely correct.i agree with you.
    Mar 2014
    S.OF.OMAN
    44
    Re: superheat
    17 psi suction and suction line temp is 7-8 degree C.... R134a gas.. FILTRINE CHILLER using for MRI machine
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    Re: superheat
    suction superheat= 15.5K
    Mar 2014
    S.OF.OMAN
    44
    Re: superheat
    is it ok sir for this chiller
    moideen's Avatar
    Apr 2008
    u.a.e
    49
    412
    Re: superheat
    Check the suction superheat value when pull down is complete and steady full load operation has been established. 15.5 is high. Bring down to 6-8k.
    Mar 2014
    S.OF.OMAN
    44
    Re: superheat
    pls mention in deg c or deg f........
    Split Croatia
    6,151
    Re: superheat
    It is already explained earlier in this thread.
    Aug 2014
    75
    508
    Re: superheat
    Hi 17psi = (minus) -8 degrees C, using R134A
    Suction pipe temperature 7 to 8 deg C
    So (minus)-8 Saturation temperature to +7 to 8 deg C actaul pipe temperture= approx15.5 degK superheat
    R134A is a very stable refrigerant and normally I would expect to get a steady superheat of between 5 and 8 deg k using a thermostatic expansion valve
    If using an Electronic expansion valve (stepper valve) I would expect a superheat of between 4 to 7deg C superheat.
    Your evaporating Pressure/Temperature ie 17psi/ (minus)-8 degC is low for an air conditioning system as AC systems normally work in the positive temps ie +5 deg C not in negative temps ie minus 8
    By opening your expansion valve a few turns you should see the suction guage rise a few psi and the suction pipe temperature should fall a few deg C.
    So in reality you should see a suction pressure of about 27psi/0 degC with an actual pipe temperature of about 6 degC .So 0degC to 6 degC = 6degK actual superheat
    This all depends if the system is fully charged , the drier is clean etc etc
    I always fit electronic expansion valves as they always give superior control,a more stable suction condition and give better system efficiency by running with a lower superheat condition thereby utilising the evaporator surface more efficiently
    Are you cooling air or water or some other fluid?
    Kr Glenn