    Re: Liquid receiver

    Quote Originally Posted by Peter_1
    NoNickName, he wants a chiller which gives no problems
    Well, charging 300Kg + of refrigerant is not the way to go for "no problems".

  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Liquid receiver

    Quote Originally Posted by NoNickName
    Well, charging 300Kg + of refrigerant is not the way to go for "no problems".
    300litres would not be 300kg with the given density it would be 360kg aproximately.

    This would not necessarily be a large charge, I have just sized the receiver for what I would call a small 404a blast freezer the net volume is about 700 litres.

    Receiver volume is based on 2/3 of the evaporator volume + the liquid line, NOT the condenser volume, the volume in the condenser is just that, pumping down the system will not change the volume in the condenser or the condensate line.


    Better an oversized receiver with less charge in it rather than a small receiver over charged.

    Kind Regards. Andy

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Liquid receiver

    Quote Originally Posted by Andy
    Receiver volume is based on 2/3 of the evaporator volume + the liquid line, NOT the condenser volume, the volume in the condenser is just that, pumping down the system will not change the volume in the condenser or the condensate line.
    If you are using head pressure controls to flood an air-cooled condenser, the volume of the condenser does matter.

    You could use the entire volume of the condenser (to calculate the mass of course) if the condenser is operating in very cold weather.

    The liquid has to go somewhere in the summer.

  4. #4
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Liquid receiver

    Quote Originally Posted by US Iceman
    If you are using head pressure controls to flood an air-cooled condenser, the volume of the condenser does matter.

    You could use the entire volume of the condenser (to calculate the mass of course) if the condenser is operating in very cold weather.

    The liquid has to go somewhere in the summer.
    Never thought of that one

    Again a very good reason for not undersizing the receiver. Generally I would use inverters on the condenser fan rather than back large amounts of liquid into the condenser, reduces the refrigerant charge.

    Kind Regards. Andy

Similar Threads

  1. Liquid receiver size
    By Volnei in forum Industrial
    Replies: 5
    Last Post: 21-04-2006, 02:16 AM
  2. Replies: 2
    Last Post: 16-11-2005, 05:34 PM
  3. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM
  4. Liquid Receiver Calculations
    By David PS in forum Fundamentals
    Replies: 6
    Last Post: 08-04-2005, 09:55 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •