This would not necessarily be a large charge, I have just sized the receiver for what I would call a small 404a blast freezer the net volume is about 700 litres.
Receiver volume is based on 2/3 of the evaporator volume + the liquid line, NOT the condenser volume, the volume in the condenser is just that, pumping down the system will not change the volume in the condenser or the condensate line.
Better an oversized receiver with less charge in it rather than a small receiver over charged.
Kind Regards. Andy
-
11-04-2006, 10:40 PM #3
Re: Liquid receiver
Originally Posted by Andy
You could use the entire volume of the condenser (to calculate the mass of course) if the condenser is operating in very cold weather.
The liquid has to go somewhere in the summer.
-
11-04-2006, 10:59 PM #4
Re: Liquid receiver
Originally Posted by US Iceman
Again a very good reason for not undersizing the receiver. Generally I would use inverters on the condenser fan rather than back large amounts of liquid into the condenser, reduces the refrigerant charge.
Kind Regards. Andy
Similar Threads
-
Liquid receiver size
By Volnei in forum IndustrialReplies: 5Last Post: 21-04-2006, 02:16 AM -
Best way to sense level of liquid refrigerant in receiver?
By star882 in forum FundamentalsReplies: 2Last Post: 16-11-2005, 05:34 PM -
Parker levels in ammonia systems
By Friobernal in forum IndustrialReplies: 3Last Post: 04-08-2005, 03:46 PM -
Liquid Receiver Calculations
By David PS in forum FundamentalsReplies: 6Last Post: 08-04-2005, 09:55 AM