Originally Posted by NoNickName
Liquid 40°C in summer and 20°C in winter will give a lower evaporationg temperature in winter conditions at the same condensing pressure??
It will increase the net effect on the evaporator a lot because teh enthaply of the liquid has increased seriously.
The COP of the compressor will increase with +/-25 to 30% and you're talking about a lower performance?
The power factor of a motor varies
according to its load. The higher the percentage of
the rated load, the higher the power factor
What is then the advantage of the digital scroll?
And form the unloader valves on larger machines and so many small semi-hermetic machines?
The net effect you gain by increasing the suction pressure by unloading is by far much higher then the negative effects of increase of the power factor.
We measured this some 15 years ago on a open 8CC compressor of DWM/Copeland and there was as far as I can remember almost no measurable difference.
And you pay - at least in Belgium - only the power you consume for smalelr applications, not the apparent power.
Line current will be a little bit higher but that's all. So if power factor rises, you could say, who cares!?
I agree on the conclusions, and on the fact that higher subcooling does not equates in better overall performanceIt's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
Similar Threads
-
Liquid receiver size
By Volnei in forum IndustrialReplies: 5Last Post: 21-04-2006, 02:16 AM -
Best way to sense level of liquid refrigerant in receiver?
By star882 in forum FundamentalsReplies: 2Last Post: 16-11-2005, 05:34 PM -
Parker levels in ammonia systems
By Friobernal in forum IndustrialReplies: 3Last Post: 04-08-2005, 03:46 PM -
Liquid Receiver Calculations
By David PS in forum FundamentalsReplies: 6Last Post: 08-04-2005, 09:55 AM