    Re: Liquid receiver

    Dossat/Horan say, When liquid refrigerant is subcooled before entering the metering device, the refrigeration effect per unit mass is increased. The example given is the heat removed (6.96btu/lbm). for the saturated cycle, in the example, the refrigeration effect per unit mass is 60.38btu/lbmas shown in a proof11.11 in section 11.6. the proof states for the sub cooled cycle, the refrigeration effect per unit mass, is 67.34btu/lb, a difference of 11.53% This is for actual refrigeration cycle
    This in turn reduces mass flow rate by 10.27% and since the mass flow rate is less for the sub cooled cycle, it follows that the volume of vaporthat the compressor must handle per unit of capacity will also be less. Going on, the compressor displacement required for the sub cooled cycle is smaller then that required for the saturated cycle because the volume of vapor per unit of capacity is less. so the COP will increase by 11.5% in the example.

  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Liquid receiver

    Quote Originally Posted by wambat
    ... so the COP will increase by 11.5% in the example.

    This is the example of how books should not be read.
    In real life we already have a compressor, a TEV and an evaporator, the three chosen for a given SC.
    In case SC is increased, there will be no COP increase and no different mass flow, because the components are still the same.
    The net enthalpy gain will become lower evap. pressure, which in turn becomes as a lower compressor suction pressure, and a lower COP.

    If the manufacturer declares data with 3°K SC, please stay with that. Any increase in SC will result in poorer performance for a given chiller.

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Liquid receiver

    Quote Originally Posted by wambat
    ....Dossat/Horan say, ..... so the COP will increase by 11.5% in the example.
    That's what I thouht and was trying to explain with no so many words.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Liquid receiver size
    By Volnei in forum Industrial
    Replies: 5
    Last Post: 21-04-2006, 02:16 AM
  2. Replies: 2
    Last Post: 16-11-2005, 05:34 PM
  3. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM
  4. Liquid Receiver Calculations
    By David PS in forum Fundamentals
    Replies: 6
    Last Post: 08-04-2005, 09:55 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •