    Non-condensable's and Sight Glass Bubbles

    Howdy to everyone...

    I'm trying to understand the effects of NCG's in high temp systems. Hours of research haven't as yet answered my question(s). I staged an "experiment" with an R22 split heat pump system (running in the cool cycle), beginning with decent performance numbers, then added a small amount of nitrogen to the system. TXV fed coil.

    Beginning numbers:

    Suction/SST...71 psig/41.6˚F
    Superheat...13˚F
    Liquid/SCT...213 psig/106˚F
    Subcooling...11˚F

    Sight glass full, located 12" downstream of liquid service valve

    After adding nitrogen:

    Suction/SST...73 psig/43˚F
    Superheat...12˚F
    Liquid/SCT...225 psig/110˚F
    Subcooling...17˚F

    Sight glass gave appearance of undercharge...less than full.

    Anyone know what causes the bubbles/voids in the sight glass, and what they are? Nitrogen or *****?
    Last edited by Saturatedpsi; 31-08-2014 at 01:45 PM. Reason: Additional data