    Question Problem with freezer fan.



    I am looking at a upright freezer for a mate.
    it is a Westinghouse 380 L frost free.

    It is cooling at the bottom where the evap is , but as it has a duct in the back with a JRM fam motor , to distribute cold air from evap to top of freezer.



    This fan does not run has 240 V in and 240 V out
    there is a red alarm light on the front indicating an alarm has gone off.

    For this freezer to defrost , i think it works on a klixon.

    What could be the causes for the fan not to run.
    Last edited by fridg; 12-04-2006 at 04:01 AM.


    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  2. #2
    Join Date
    Nov 2005
    Location
    USA
    Posts
    211
    Rep Power
    19

    Re: Problem with freezer fan.

    Is there voltage at the motor? Can the fan be manually turned? Is the motor fine? Are the caps (if any) fine?
    "If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine

  3. #3
    Join Date
    Nov 2005
    Location
    australia
    Posts
    152
    Rep Power
    19

    Re: Problem with freezer fan.

    Yes 240 V both sides of motor.

    The motor can be turned (not ceased)

    Resistance of motor is 240 ohms

    No caps.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  4. #4
    Join Date
    Aug 2005
    Location
    iraq
    Age
    67
    Posts
    131
    Rep Power
    19

    Re: Problem with freezer fan.

    now i beleive that the motor have burning coil
    no other cause i can figer out

  5. #5
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Problem with freezer fan.

    Quote Originally Posted by fridg
    Yes 240 V both sides of motor.

    The motor can be turned (not ceased)

    Resistance of motor is 240 ohms

    No caps.
    G'day fridg

    Are you checking to earth and to each side of the motor.?

    Check across the motor and see what you get.

    If your getting 240v to earth BOTH sides the door switch is probably switching a nuetral and is open.
    Last edited by Temprite; 11-04-2006 at 09:56 AM.

  6. #6
    Join Date
    Nov 2005
    Location
    australia
    Posts
    152
    Rep Power
    19

    Re: Problem with freezer fan.

    Quote Originally Posted by Temprite
    G'day fridg

    Are you checking to earth and to each side of the motor.?

    Check across the motor and see what you get.

    If your getting 240v BOTH sides the door switch is probably switching a nuetral and is open.

    Temprite

    I am checking this voltage to earth.


    There is no door switch on the freezer , sounds funny but i had a real good look for one.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  7. #7
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Problem with freezer fan.

    Dogma

    I just edited my previous post.

    If you are getting 240v to earth both sides of the motor you are not getting a nuetral to the motor.In other words there is a switch open probably.(Door switch,defrost timer).

    Check across the motor.

  8. #8
    Join Date
    Nov 2005
    Location
    australia
    Posts
    152
    Rep Power
    19

    Re: Problem with freezer fan.

    Quote Originally Posted by Temprite
    Dogma

    I just edited my previous post.

    If you are getting 240v to earth both sides of the motor you are not getting a nuetral to the motor.In other words there is a switch open probably.(Door switch,defrost timer).

    Check across the motor.

    How do i test the klixon or defrost heater

    to see if it is open or closed circut
    the fan runs through the defrost heater or klixon.

    From my initial tests with the compressor running , the evap fan should be on too , as there is no switch inside the cabinet.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  9. #9
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Problem with freezer fan.

    G'day fridg.

    Fan is getting its nuetral through the defrost heater.

    Unplug heater and check resistance if open circuited fan will not be able to get nuetral.

    Same with klixon it may be staying open.

    But if your gas charge is low the klixon will stay open.

    Alternatively
    Put one side of meter on fan motor and check voltage to klixon, then heater and when you get 240v you then know that you now have a nuetral and you will be able to determine where the break is.

  10. #10
    Join Date
    Nov 2005
    Location
    australia
    Posts
    152
    Rep Power
    19

    Re: Problem with freezer fan.

    Thanks mate

    I owe you a beer.
    Last edited by fridg; 12-04-2006 at 04:02 AM.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  11. #11
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Problem with freezer fan.

    No probs.

    Let me know how it goes.

  12. #12
    Join Date
    Nov 2005
    Location
    USA
    Posts
    211
    Rep Power
    19

    Re: Problem with freezer fan.

    If you are getting 240v to earth both sides of the motor you are not getting a nuetral to the motor.In other words there is a switch open probably.(Door switch,defrost timer).
    Switches should always be on the hot side. IIRC, it's against code to install switches in the neutral. Check for bad connections and improper wiring.
    "If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine

  13. #13
    Join Date
    Nov 2005
    Location
    australia
    Posts
    152
    Rep Power
    19

    Re: Problem with freezer fan.

    Ok installed the new fan motor

    The fan does not run when in circut with the heater element and the heater switch.

    when i take these out of the circut , and put the fan in the circut before the heater it runs.

    Now i have been told by my supply house that this fan will not run until the evap coil is down to temp.

    So i have been forced to wait 24 hrs.

    Also my guys on the inside have told me never touch a ******* domestic , run away.


    I am an apprentice at a large manufacturing firm so the only experience i get on stuff is on the side.

    But now i have to look at another domestic freezer with the same problem i think , no evap fan.

    And the inside guys quote keeps running through my head "never touch a ******* domestic"
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

  14. #14
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Problem with freezer fan.

    G'day Dogma

    Quote Originally Posted by Temprite
    But if your gas charge is low the klixon will stay open.
    Because it is not cold enough......

    Did you find what part of the circuit was open?

  15. #15
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Problem with freezer fan.

    Quote Originally Posted by star882
    Switches should always be on the hot side. IIRC, it's against code to install switches in the neutral. Check for bad connections and improper wiring.
    Might be against code but you still see it.

  16. #16
    Join Date
    Nov 2005
    Location
    australia
    Posts
    152
    Rep Power
    19

    Re: Problem with freezer fan.

    Ok here is the story

    The first freezer i replaced the evap fan motor , and left for 24 hrs to pull down , has come back to life and is freezing like a true champion.

    It was a faulty evap fan motor.




    Now on the second freezer

    My tests indicated to me that the defrost terminator (klixon) was faulty
    went to my supply house picked up a similar terminator

    have gone back to job to install , decided to check main lead for insulation faults , well blow me down it is failing now.

    Checked compressor , now this puppy has ceased because it was turned off over night.


    And the quote returns "never touch a ******* domestic"
    Last edited by fridg; 13-04-2006 at 02:13 AM.
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.

Similar Threads

  1. Blast freezer temperature problem. Please help!!!
    By volta in forum Technical Discussions
    Replies: 13
    Last Post: 10-05-2010, 04:54 AM
  2. Strange problem
    By Peter_1 in forum Electrical
    Replies: 9
    Last Post: 10-04-2007, 05:19 PM
  3. please help with Kenmore Upright Freezer
    By lrn376 in forum Trouble Shooting
    Replies: 0
    Last Post: 09-07-2006, 10:40 PM
  4. Condensation Problem At Door to Freezers
    By mmarch in forum Air Conditioning
    Replies: 5
    Last Post: 17-10-2005, 02:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •