11-04-2006, 04:27 AM #1
Problem with freezer fan.
I am looking at a upright freezer for a mate.
it is a Westinghouse 380 L frost free.
It is cooling at the bottom where the evap is , but as it has a duct in the back with a JRM fam motor , to distribute cold air from evap to top of freezer.
This fan does not run has 240 V in and 240 V out
there is a red alarm light on the front indicating an alarm has gone off.
For this freezer to defrost , i think it works on a klixon.
What could be the causes for the fan not to run.Last edited by fridg; 12-04-2006 at 04:01 AM.
The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.
-
11-04-2006, 04:42 AM #2
Re: Problem with freezer fan.
Is there voltage at the motor? Can the fan be manually turned? Is the motor fine? Are the caps (if any) fine?
"If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine
-
11-04-2006, 04:48 AM #3
Re: Problem with freezer fan.
Yes 240 V both sides of motor.
The motor can be turned (not ceased)
Resistance of motor is 240 ohms
No caps.The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.
-
11-04-2006, 09:16 AM #4
Re: Problem with freezer fan.
now i beleive that the motor have burning coil
no other cause i can figer out
-
11-04-2006, 09:24 AM #5
Re: Problem with freezer fan.
Originally Posted by fridg
Are you checking to earth and to each side of the motor.?
Check across the motor and see what you get.
If your getting 240v to earth BOTH sides the door switch is probably switching a nuetral and is open.Last edited by Temprite; 11-04-2006 at 09:56 AM.
-
11-04-2006, 09:45 AM #6
Re: Problem with freezer fan.
Originally Posted by Temprite
Temprite
I am checking this voltage to earth.
There is no door switch on the freezer , sounds funny but i had a real good look for one.The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.
-
11-04-2006, 10:03 AM #7
Re: Problem with freezer fan.
Dogma
I just edited my previous post.
If you are getting 240v to earth both sides of the motor you are not getting a nuetral to the motor.In other words there is a switch open probably.(Door switch,defrost timer).
Check across the motor.
-
11-04-2006, 10:51 PM #8
Re: Problem with freezer fan.
If you are getting 240v to earth both sides of the motor you are not getting a nuetral to the motor.In other words there is a switch open probably.(Door switch,defrost timer)."If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine
-
12-04-2006, 04:11 AM #9
Re: Problem with freezer fan.
Ok installed the new fan motor
The fan does not run when in circut with the heater element and the heater switch.
when i take these out of the circut , and put the fan in the circut before the heater it runs.
Now i have been told by my supply house that this fan will not run until the evap coil is down to temp.
So i have been forced to wait 24 hrs.
Also my guys on the inside have told me never touch a ******* domestic , run away.
I am an apprentice at a large manufacturing firm so the only experience i get on stuff is on the side.
But now i have to look at another domestic freezer with the same problem i think , no evap fan.
And the inside guys quote keeps running through my head "never touch a ******* domestic"The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.
-
12-04-2006, 12:42 PM #10
Re: Problem with freezer fan.
Originally Posted by star882
-
13-04-2006, 01:51 AM #11
Re: Problem with freezer fan.
Ok here is the story
The first freezer i replaced the evap fan motor , and left for 24 hrs to pull down , has come back to life and is freezing like a true champion.
It was a faulty evap fan motor.
Now on the second freezer
My tests indicated to me that the defrost terminator (klixon) was faulty
went to my supply house picked up a similar terminator
have gone back to job to install , decided to check main lead for insulation faults , well blow me down it is failing now.
Checked compressor , now this puppy has ceased because it was turned off over night.
And the quote returns "never touch a ******* domestic"Last edited by fridg; 13-04-2006 at 02:13 AM.
The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.
Similar Threads
-
Blast freezer temperature problem. Please help!!!
By volta in forum Technical DiscussionsReplies: 13Last Post: 10-05-2010, 04:54 AM -
Strange problem
By Peter_1 in forum ElectricalReplies: 9Last Post: 10-04-2007, 05:19 PM -
please help with Kenmore Upright Freezer
By lrn376 in forum Trouble ShootingReplies: 0Last Post: 09-07-2006, 10:40 PM -
Condensation Problem At Door to Freezers
By mmarch in forum Air ConditioningReplies: 5Last Post: 17-10-2005, 02:42 PM