Results 1 to 6 of 6

Thread: superheat

  1. #1
    Join Date
    Mar 2014
    Location
    S.OF.OMAN
    Age
    43
    Posts
    36
    Rep Power
    0

    superheat



    can anybody tell what is the normal suction superheat of R134a gas in central air conditioning system..???



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: superheat

    3K useful superheat and 3K non useful = 6K

  3. #3
    Join Date
    Mar 2014
    Location
    S.OF.OMAN
    Age
    43
    Posts
    36
    Rep Power
    0

    Re: superheat

    frank.... i dnt understand

  4. #4
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23
    5-10k rule of thumb

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: superheat

    Quote Originally Posted by Shajan John View Post
    frank.... i dnt understand
    3K usefull is at evaporator outlet
    3k unusefull is at suction line from evaporator to compressor

  6. #6
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    48
    Posts
    412
    Rep Power
    22

    Re: superheat

    Quote Originally Posted by Shajan John View Post
    frank.... i dnt understand
    for undestanding useful and nonuseful superheat, go to this link

    http://www.refrigeration-engineer.co...eful-Superheat