Hi guys, installing a 14kw daikin RZQG140L7V1 , itis one outdoor and twin indoor each 7kw. my question is not about the positioning, my question is : do i need to reduce 5/8 or not, i mean i enter from outdoor with 5/8 to refnet, do i use 5/8 from the refnet to coolers or do i need to reduce the pipe size? same for liquid line? if i do not reduce the refnet becomes evap due to pressure drop at the joint.
any help will be appriciated
Sork
-
23-08-2014, 10:44 PM #2
Re: refnet joint reducer
whatever pipe size is on the outdoor - run that size to your refnet/branch, then for a 7 kw daikin, should be 5/8 3/8 from each branch to each indoor- branch should be ideally equal lengths on each branch- and also have a max of 15mtr total on the branches
-
23-08-2014, 10:47 PM #3
Re: refnet joint reducer
5/8 3/8 (15mm ,10mm pipework on outdoor too)
http://www.daikintech.co.uk/Data/Spl...B_Databook.pdf
page 27 shows pipe layout for a twin
-
24-08-2014, 06:37 AM #4
Re: refnet joint reducer
Well said Monkey...
And don't forget to only wire the BRC controller to 1of the indoor fan coils otherwise you will get an error.
-
24-08-2014, 03:34 PM #5
Re: refnet joint reducer
Thanks Monk, greatly appriciated, only limited hours i can be on the site. i only need to keep the distance of the coolers to refnet equal, this is simple enough; then, after the joint i follow the evaporators inlet pipe size.
-
24-08-2014, 03:35 PM #6
Re: refnet joint reducer
thank you Frank.
-
25-08-2014, 08:41 PM #7
Re: refnet joint reducer
i have checked the coolers pipe, as you said rightly, it is 5/8 and 3/8 so i connect the refnet 8 metres to each cooler with 5/8 and 3/8 . i have not yet seen the outdoor pipe size. my question is if that is 5/8 and 3/8 same as coolers, from condensing unit to refnet, would not there be a pressure drop? or maybe pipe size of the condensing unit is larger!
Last edited by sork; 25-08-2014 at 09:03 PM. Reason: correction
-
25-08-2014, 08:48 PM #8
Re: refnet joint reducer
the manual states 5/8 3/8 on the outdoor, all daikin 410 units from 7kw upwards are 5/8 3/8 - so it seems strange but trust me it works,
-
25-08-2014, 09:07 PM #9
Re: refnet joint reducer
you mean i connect to refnet 5/8 and 3/8 from the condenser? then from refnet to coolers on 5/8 and 3/8 as well? so you think there will be no pressure drop in the refnet? if i keep the distance from the refnet to the cooles the same length?
-
25-08-2014, 11:09 PM #10
Re: refnet joint reducer
Also make sure that you mount the refnet correctly.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
27-08-2014, 08:24 AM #11
Re: refnet joint reducer
yes horizantal or vertical, in this case twin 7kw coolers , there are no reduction in pipe size enter 5/8 from the condensing unit; leave 5/8 same for discharge line on 3/8. approximatly same distance from the refnet to coolers.
-
07-10-2014, 01:24 PM #12