    refnet joint reducer



    Hi guys, installing a 14kw daikin RZQG140L7V1 , itis one outdoor and twin indoor each 7kw. my question is not about the positioning, my question is : do i need to reduce 5/8 or not, i mean i enter from outdoor with 5/8 to refnet, do i use 5/8 from the refnet to coolers or do i need to reduce the pipe size? same for liquid line? if i do not reduce the refnet becomes evap due to pressure drop at the joint.
    any help will be appriciated
    Sork



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: refnet joint reducer

    whatever pipe size is on the outdoor - run that size to your refnet/branch, then for a 7 kw daikin, should be 5/8 3/8 from each branch to each indoor- branch should be ideally equal lengths on each branch- and also have a max of 15mtr total on the branches

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: refnet joint reducer

    5/8 3/8 (15mm ,10mm pipework on outdoor too)
    http://www.daikintech.co.uk/Data/Spl...B_Databook.pdf
    page 27 shows pipe layout for a twin

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: refnet joint reducer

    Well said Monkey...
    And don't forget to only wire the BRC controller to 1of the indoor fan coils otherwise you will get an error.

  5. #5
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: refnet joint reducer

    Thanks Monk, greatly appriciated, only limited hours i can be on the site. i only need to keep the distance of the coolers to refnet equal, this is simple enough; then, after the joint i follow the evaporators inlet pipe size.

  6. #6
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: refnet joint reducer

    thank you Frank.

  7. #7
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: refnet joint reducer

    i have checked the coolers pipe, as you said rightly, it is 5/8 and 3/8 so i connect the refnet 8 metres to each cooler with 5/8 and 3/8 . i have not yet seen the outdoor pipe size. my question is if that is 5/8 and 3/8 same as coolers, from condensing unit to refnet, would not there be a pressure drop? or maybe pipe size of the condensing unit is larger!
    Last edited by sork; 25-08-2014 at 09:03 PM. Reason: correction

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: refnet joint reducer

    the manual states 5/8 3/8 on the outdoor, all daikin 410 units from 7kw upwards are 5/8 3/8 - so it seems strange but trust me it works,

  9. #9
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: refnet joint reducer

    you mean i connect to refnet 5/8 and 3/8 from the condenser? then from refnet to coolers on 5/8 and 3/8 as well? so you think there will be no pressure drop in the refnet? if i keep the distance from the refnet to the cooles the same length?

  10. #10
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: refnet joint reducer

    Also make sure that you mount the refnet correctly.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  11. #11
    Join Date
    Jun 2008
    Location
    london
    Age
    63
    Posts
    115
    Rep Power
    16

    Re: refnet joint reducer

    yes horizantal or vertical, in this case twin 7kw coolers , there are no reduction in pipe size enter 5/8 from the condensing unit; leave 5/8 same for discharge line on 3/8. approximatly same distance from the refnet to coolers.

  12. #12
    Join Date
    Oct 2014
    Location
    United States
    Age
    31
    Posts
    2
    Rep Power
    0

    Re: refnet joint reducer

    Useful share. Thanks for the helpful information.