    Water Chiller Technical Specification and Cable/Breaker Sizing



    Dear fellow ,I am confused by technical specs of chiller and installed cable and breaker rating.
    Following technical specs are written in chiller docs.

    Absorbed Power = 86 KW

    Nominal operating current = 145 A

    Max operating current = 244 A


    Now which of above parameter should be used for cable and breaker sizing? .

    It is worthy to mention that chiller is water cooled twin screw compression chiller.

    I have found that contractor has used 70 mm2 cable and 400 A rating breaker.

    Please share your expert views as I suspect that above sizing is not compatible with chiller rating.



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Water Chiller Technical Specification and Cable/Breaker Sizing

    look at lra - locked rotor ampage, your lenght of cable run, type of cable used, whether its in free air, will determine your cable size, the fuses are designed to protect the cable from melting
    see the link
    http://www.openelectrical.org/wiki/i...ng_Calculation

  3. #3
    Join Date
    Jun 2012
    Location
    Pakistan
    Posts
    44
    Rep Power
    0

    Re: Water Chiller Technical Specification and Cable/Breaker Sizing

    Quote Originally Posted by install monkey View Post
    look at lra - locked rotor ampage, your lenght of cable run, type of cable used, whether its in free air, will determine your cable size, the fuses are designed to protect the cable from melting
    see the link
    http://www.openelectrical.org/wiki/i...ng_Calculation
    Can I take maximum operating current as LRA?
    The only information I have in this case is mentioned above .
    plz help in this case .

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Water Chiller Technical Specification and Cable/Breaker Sizing

    whats the make/model number of the chiller?, theres no harm in oversizing the cable -apart from the additional cost

  5. #5
    Join Date
    Jun 2012
    Location
    Pakistan
    Posts
    44
    Rep Power
    0

    Re: Water Chiller Technical Specification and Cable/Breaker Sizing

    Quote Originally Posted by install monkey View Post
    whats the make/model number of the chiller?, theres no harm in oversizing the cable -apart from the additional cost
    Chiller model : Interklima (Greece) WWC-105

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Water Chiller Technical Specification and Cable/Breaker Sizing

    ive checked the sales info and doesnt state any compressor reference to check lra
    best to contact the sales office as if your going to be buying 1 then they should provide you with an installation manual prior to ordering


    Contact


    70o klm Athens - LamiaHalkidaPO 191 73 34 100 Greece

    +30 2262085600
    +30 2262085728


    http://www.interklima.gr

  7. #7
    Join Date
    Jun 2012
    Location
    Pakistan
    Posts
    44
    Rep Power
    0

    Re: Water Chiller Technical Specification and Cable/Breaker Sizing

    Let I put in simple what I intended to ask. (For the time
    being put all other things aside, plz )Theoretically which of following parameter is considered for breaker/cable sizing?

    Absorbed Power = 86 KW

    Nominal operating current = 145 A

    Max operating current = 244 A

  8. #8
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Water Chiller Technical Specification and Cable/Breaker Sizing

    max operating current
    Quote Originally Posted by pakblogger2012 View Post
    Let I put in simple what I intended to ask. (For the time
    being put all other things aside, plz )Theoretically which of following parameter is considered for breaker/cable sizing?

    Absorbed Power = 86 KW

    Nominal operating current = 145 A

    Max operating current = 244 A

  9. #9
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,444
    Rep Power
    37

    Re: Water Chiller Technical Specification and Cable/Breaker Sizing

    Voltage: 400V


    Load: 221.7kW / 400A


    Length: 20m


    Method of Installation: Clipped direct

    Cable Size: 150mm˛

  10. #10
    Join Date
    Jun 2012
    Location
    Pakistan
    Posts
    44
    Rep Power
    0

    Re: Water Chiller Technical Specification and Cable/Breaker Sizing


  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Water Chiller Technical Specification and Cable/Breaker Sizing

    Cable is sized according to start method of compressors, allowable voltage drop, cable length, placement, ambient conditions and many more factors influencing proper function of Chiller.
    Therefore, it is job for electrical engineer to make calculation and other details for correct cable size choice and installation.

    Breaker is sized according to chosen cable and type is chosen according to maximum starting current and duration of start condition.
    Last edited by nike123; 24-08-2014 at 09:34 PM.