20-08-2014, 10:49 PM #1
mc quay chiller air cooled flooded ooil screw compressor
Any onr can help on mc quay chiller agr 212. Flooded oil single screw compressor
I do believe we added extra oil . Was working for few days then packed. Now it starts 05 second and shut down. I cant see any faults on the microtech 2 control panel sudden shut down .
I have diagnosis. And the answers but i need reinsurrance. Flush gas liquid imigrates into the oil
Evaporaror flooded oil. Filter blocked. But the sign are on the filter drier shraded valve trace of oil during pressure reading . The oil separator was a hot but after 05sec of. Start become very cold condenser pressure 05 bar. Evap 2.5 bar on r134a. Please i ve tryed to start it again. Manually but i cannot do it any suggestion.
20-08-2014, 10:52 PM #2
Re: mc quay chiller air cooled flooded ooil screw compressor
Could any one now from which site glass to check the oil level on the oil separator. Tank on quay agr al 212. Top or the button and when when the systen on or off taa
21-08-2014, 06:31 AM #3
I would suggest that you drain the oil and then refill to the correct amount
21-08-2014, 12:12 PM #4
Thanks the job done for future reference i would like to khow