    High PD on Remote Condensing Airedale Easicool R410A



    Good Evening,

    I have a problem at one of my establishments with a high PD, probably due to incorrect pipe size.
    I am about to change the pipe size and hopefully correct the error.

    How do i access the Admin controls in order to start the unit up and measure the PD again before Airedale come out to re-commission.

    Does anyone on here have experience with these systems??



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: High PD on Remote Condensing Airedale Easicool R410A

    are you sure its down to incorrect pipesize?- refer to the installation manual to check length of run, check temp diff /pressure drop accross drier, 4648 is ur standard access to adj setpoints 0113 is ur supervisor level

  3. #3
    Join Date
    Aug 2014
    Location
    A, A
    Age
    36
    Posts
    2
    Rep Power
    0

    Re: High PD on Remote Condensing Airedale Easicool R410A

    Pipe Length - 59m (20mVertical) with 13Bends
    Test results - 36.5Bar Dis, 32.5Bar Liq

    Current Pipe sizes are 1/2"Liq, 5/8" Dis
    17kw unit

    Airedale have said that the pipe sizes are to small

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: High PD on Remote Condensing Airedale Easicool R410A

    as long as the manufacturers have stated the pipe sizes are wrong, did they specify the correct size,for that run