    York millenium recip chiller fault



    Hi guys! pls help me with this fault from York millenium recip chiller, YAEP model. The unit doesn't start. it shows "REPROGRAM TYPE OF REFRIGERANT TO RUN". it needs access code to change the type of refrigerant..



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: York millenium recip chiller fault

    er662,
    tell me has the chiller been commissioned ?= sedgy

  3. #3
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: York millenium recip chiller fault

    How old is chiller?
    Mostly found in the southern part of this green and pleasant land.

  4. #4
    Join Date
    Aug 2014
    Location
    UAE
    Posts
    2
    Rep Power
    0

    Re: York millenium recip chiller fault

    it's a six-yr old chiller

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: York millenium recip chiller fault

    It may be that the battery on the micro board has failed, normally this message only appears when chiller is first switched on, you may need to change other settings if the memory has failed, each time power is lost then this will reoccur, would you not be happier to contact local York office to check it for you?
    Mostly found in the southern part of this green and pleasant land.