    Carrier 30HZ 065 pro-dialog



    Hello All,

    Can anyone tell me how to change circuit A & B lead lag operation. I have the manual and have tried everything. Can anyone let me know if I am dumb as a bag of hammers or have I a problem.

    Cheers



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Carrier 30HZ 065 pro-dialog

    Hi CuGe
    sorry little experience with this plant, but you need the controller manual and the sytem pass word to change the lead lag.

    Try putting the first circuits compressors off on service, the second set will take the load and then put the first set back on line after this.

    Still think U need the manual

    Kind Regards. Andy

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Carrier 30HZ 065 pro-dialog

    CuGe

    Try this link -
    http://www.carrier.com.lb/products/C...prodiagxhx.htm
    and click on the Technical Information link at the bottom right of the screen; this will give you access to the Pro-Logic manual as a pdf download (4.32mb).

    I think it is around page 24 that it gives the configuration instructions to change the lead/lag of the machine.

    Hope this helps.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Sep 2005
    Location
    Australia
    Age
    50
    Posts
    33
    Rep Power
    0

    Re: Carrier 30HZ 065 pro-dialog

    if it is a pd4 (white) -> user1 menu -> item 1 ->

    0 means - automatic
    1 means - lead A
    2 means - lead B
    ------------------------
    if earlier (black) -> configuration menu -> intem 2

    0 means - automatic
    1 means - lead A
    2 means - lead B
    (same as above)
    Last edited by hiitsme; 11-04-2006 at 12:54 PM.

  5. #5
    Join Date
    Sep 2005
    Location
    Australia
    Age
    50
    Posts
    33
    Rep Power
    0

    Re: Carrier 30HZ 065 pro-dialog

    you can reach these menus only if the unit is LOFF mode.

Similar Threads

  1. carrier fault codes
    By richelli in forum Trouble Shooting
    Replies: 5
    Last Post: 18-06-2010, 07:35 AM
  2. Carrier Water Chillers
    By Latte in forum Air Conditioning
    Replies: 10
    Last Post: 11-10-2008, 08:43 PM
  3. Carrier chiller oil migration
    By lowtech in forum Industrial
    Replies: 5
    Last Post: 30-04-2006, 04:11 PM
  4. carrier remote
    By superswill in forum Trouble Shooting
    Replies: 2
    Last Post: 26-04-2006, 09:17 PM
  5. Carrier spares
    By daddymac in forum Air Conditioning
    Replies: 6
    Last Post: 21-03-2006, 08:54 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •