Results 1 to 13 of 13
    Sep 2010
    yemen
    Internal Leakage In Brazed Heat Exchanger
    Please in need your help in Internal Leakage In Brazed Heat Exchanger
    3,356
    Re: Internal Leakage In Brazed Heat Exchanger
    Alamda, pretty sure it cannot be repaired, so you need a new one.
    Best to find out what caused it, freeze up, poor flow etc.
    Is the leak on refrigerant side?
    Sep 2010
    yemen
    yes , in refrigerant side to the water tank side
    i fond oil in the water tank
    Sep 2010
    yemen
    can you explaine more to me the resonse , what caused it?
    Dec 2010
    Toronto, Canada
    1,454
    Poor internal brazing or a freezeup on the water side caused by a pump failure (possibly). I've see it many times. What brand of HX and what position is it placed?
    Oct 2007
    Republic of south africa
    49
    184
    In rarer cases I have met cavitation and corrossive water chemistry together with other conditions mentioned above played a part in causing leakages in heat exchangers.
    Sep 2010
    yemen
    thanks for reply and the model of exchanger GBH500H-AE-60 and i installed its new after tow weeks leakages
    Dec 2010
    Toronto, Canada
    1,454
    Quote Originally Posted by alamda View Post
    Any pump failures or other conditions that could cause freezing on the water side? If not, it will most likely be a manufacturing problem. Two weeks is too short a time for most chemical issues.
    Auckland
    74
    3,357
    37
    Braised plate HXs do not like rapid cyclic temp changes as stainless partitions will crack and fail, I have killed a few, so now stipulate double wall and reduce the failure rates. On larger applications the re-stackable versions.
    Sep 2010
    yemen
    Quote Originally Posted by MikeHolm View Post
    Only one times freezing up on the ***** side in the suction line up from the HXs to the compressor its like snow
    Sep 2010
    yemen
    one times its
    Enough to damage the HXs?
    Sep 2010
    yemen
    what do you mean ?
    u mean the Braised plate HXs its not good and cracks occur
    Dec 2010
    Toronto, Canada
    1,454
    If you go many times from heating to cooling, for example, without enough time to gradually evenly heat up or cool down the entire HX, it can cause stresses that break the stainless.
    Each application has a HX that is right for it. It may be "plate and frame" with gaskets or brazed, or "shell and tube".