    Internal Leakage In Brazed Heat Exchanger



    Please in need your help in Internal Leakage In Brazed Heat Exchanger



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Internal Leakage In Brazed Heat Exchanger

    Alamda, pretty sure it cannot be repaired, so you need a new one.
    Best to find out what caused it, freeze up, poor flow etc.

    Is the leak on refrigerant side?

  3. #3
    Join Date
    Sep 2010
    Location
    yemen
    Posts
    16
    Rep Power
    0

    Re: Internal Leakage In Brazed Heat Exchanger

    yes , in refrigerant side to the water tank side
    i fond oil in the water tank

  4. #4
    Join Date
    Sep 2010
    Location
    yemen
    Posts
    16
    Rep Power
    0

    Re: Internal Leakage In Brazed Heat Exchanger

    can you explaine more to me the resonse , what caused it?

  5. #5
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Internal Leakage In Brazed Heat Exchanger

    Poor internal brazing or a freezeup on the water side caused by a pump failure (possibly). I've see it many times. What brand of HX and what position is it placed?

  6. #6
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    49
    Posts
    184
    Rep Power
    20

    Re: Internal Leakage In Brazed Heat Exchanger

    In rarer cases I have met cavitation and corrossive water chemistry together with other conditions mentioned above played a part in causing leakages in heat exchangers.

  7. #7
    Join Date
    Sep 2010
    Location
    yemen
    Posts
    16
    Rep Power
    0

    Re: Internal Leakage In Brazed Heat Exchanger

    thanks for reply and the model of exchanger GBH500H-AE-60 and i installed its new after tow weeks leakages

  8. #8
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Internal Leakage In Brazed Heat Exchanger

    Quote Originally Posted by alamda View Post
    thanks for reply and the model of exchanger GBH500H-AE-60 and i installed its new after tow weeks leakages
    Any pump failures or other conditions that could cause freezing on the water side? If not, it will most likely be a manufacturing problem. Two weeks is too short a time for most chemical issues.

  9. #9
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Internal Leakage In Brazed Heat Exchanger

    Braised plate HXs do not like rapid cyclic temp changes as stainless partitions will crack and fail, I have killed a few, so now stipulate double wall and reduce the failure rates. On larger applications the re-stackable versions.

  10. #10
    Join Date
    Sep 2010
    Location
    yemen
    Posts
    16
    Rep Power
    0

    Re: Internal Leakage In Brazed Heat Exchanger

    Quote Originally Posted by MikeHolm View Post
    Any pump failures or other conditions that could cause freezing on the water side? If not, it will most likely be a manufacturing problem. Two weeks is too short a time for most chemical issues.
    Only one times freezing up on the ***** side in the suction line up from the HXs to the compressor its like snow

  11. #11
    Join Date
    Sep 2010
    Location
    yemen
    Posts
    16
    Rep Power
    0

    Re: Internal Leakage In Brazed Heat Exchanger

    Quote Originally Posted by alamda View Post
    Only one times freezing up on the ***** side in the suction line up from the HXs to the compressor its like snow
    Only one times freezing up on the ***** side in the suction line up from the HXs to the compressor its like snow

    one times its
    Enough to damage the HXs?

  12. #12
    Join Date
    Sep 2010
    Location
    yemen
    Posts
    16
    Rep Power
    0

    Re: Internal Leakage In Brazed Heat Exchanger

    Quote Originally Posted by Magoo View Post
    Braised plate HXs do not like rapid cyclic temp changes as stainless partitions will crack and fail, I have killed a few, so now stipulate double wall and reduce the failure rates. On larger applications the re-stackable versions.
    what do you mean ?
    u mean the Braised plate HXs its not good and cracks occur

  13. #13
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Internal Leakage In Brazed Heat Exchanger

    If you go many times from heating to cooling, for example, without enough time to gradually evenly heat up or cool down the entire HX, it can cause stresses that break the stainless.

    Each application has a HX that is right for it. It may be "plate and frame" with gaskets or brazed, or "shell and tube".