    Eveining all im wondering if there is a way of accessing the coil probe on this type on controller i looked at 1 briefly today and it was iced up defrosted it and let it come back on i noticed though the evap fan would run for a minute the switch off as if short of gas but i couldnt access the 2nd peobe to check coil temp i have the paperwork but im goimg back to it tomorrow to check everything thamks



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: dixell xr06 controller

    fan start parameter, if the cab is warm, evap fan will cycle on/off till it gets to grips with the load- when the cab is at temp the fan will operate in a more stable manner

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

  4. #4
    Join Date
    Mar 2011
    Location
    england
    Age
    34
    Posts
    101
    Rep Power
    14

    Re: dixell xr06 controller

    Thanks install monkey i noticed the ice was formed right around the drip tray of the evap but there is one of those heater mats on the drip yray so i wonder if it failed any body else got advice its not exactly a reputable cabinet name either

  5. #5
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: dixell xr06 controller

    Don't like dixell,,eliwell every time for me!