    low pressure is very high, high pressure is on the low side?!?



    I have just finished installing a Bryant R410Asystem (Condenser and Cooling coil).
    See picture of the gauge reading (low pressure is very high, high pressure is on the low side; subcooling is where it should be (according to Bryant chart)) and the the temperature differential inside is 16-17 degree Fahrenheit. The client complains it's not cooling enough and not cooling fast enough compared to his previous R22 system.
    What can the problem/s be?
    What should I do to fix it/them?
    Thanks

    Low 132 psi
    High 285psi
    Low side sensor temp 77F
    Superheat 32F
    High side sensor temp 83F
    Sub cool 9F
    2014-08-12_13-54-33_82.jpg



  2. #2
    Join Date
    Oct 2013
    Location
    singapore
    Posts
    11
    Rep Power
    0

    Re: low pressure is very high, high pressure is on the low side?!?

    the low side looks normal to me but high side is pretty low when we reference with 410a. btw yours is dx or vrv.