    compressor burned 4 capacitors



    Hi
    i get a call from my friend
    he said that his 24000 btu split ac unit had bad capacitor
    so he replaced it with same size and specification
    he said the unit worked perfectly for 30 min then stopeed working
    so he replaced the capacitor again and the unit worked for 30 minutes then stopped working
    then replaced for third time then forth time with same result
    the compressor is rotary type
    made by LG



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: compressor burned 4 capacitors

    And the measured running current of the compressor is?


  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: compressor burned 4 capacitors

    Did he test the capacitors or just guess that they were at fault?

  4. #4
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,492
    Rep Power
    24

    Re: compressor burned 4 capacitors

    One definition of insanity is performing the same task over and over and expecting a different result, haha. I can maybe see changing it once without checking the current draw, but 3 times?

  5. #5
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    624
    Rep Power
    16

    Re: compressor burned 4 capacitors

    i will ask him then reply u

  6. #6
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    48
    Posts
    186
    Rep Power
    20

    Re: compressor burned 4 capacitors

    Most likely caused by compressor drawing excessively high current.

  7. #7
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: compressor burned 4 capacitors

    With the situation Iraq is in at this time, i'm thinking a stable power grid might be a problem. Low or fluctuation voltage.