    Midea 36000 too hot condenser and overload after few hours problem.



    hi. Dear friends.
    I have Strange problem with midea air condiditioner that condenser become too hot and compressor draw high ampere about 20 21 with 60 psi with r22 gases.
    Current witch printed in nameplate is about 17 and rated current is 25 A.
    If we increase gas the drawn ampere increase and Cause compressor overload.
    In 60 psi after few hour compressor overloaded Basr on weather condition.
    I changed cpacitors( it has 2 Capacitor with 60 mf) and used presure nh3 to clean air conditioner evaporator and condenser but nothing changed.
    please help me to know what is problem.
    It has capilary tube.



  2. #2
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    624
    Rep Power
    16

    Re: Midea 36000 too hot condenser and overload after few hours problem.

    did u check the 4 way valve
    is the compressor good?

  3. #3
    Join Date
    Apr 2008
    Location
    iran
    Posts
    9
    Rep Power
    0

    Re: Midea 36000 too hot condenser and overload after few hours problem.

    Air conditioner installed 3 month air ago and compressor has sufficient power and can cool inside store.
    no I didn't check the 4way valve But could you pleaseexplain the impact of 4way valve in my problem?

  4. #4
    Join Date
    Apr 2012
    Location
    Iraq
    Age
    35
    Posts
    624
    Rep Power
    16

    Re: Midea 36000 too hot condenser and overload after few hours problem.

    if pressure increase abnormally this could be the 4 way valve is faulty
    or that could be result of condensor fan faulty
    the unit was new?
    Last edited by kefah; 12-08-2014 at 07:39 PM.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Midea 36000 too hot condenser and overload after few hours problem.

    Just giving compressor amp draw and suction pressure does not give us a clear picture of what is happening on you system.

    Can you take more measurements around the system and post them on here?

    Discharge pressure
    air temp on to the condenser
    air temp off the condenser
    liquid line temperature
    liquid line pressure
    suction line pressure
    suction line temperature
    evaporator air on temperature
    evaporator air off temperature
    ambient temperature

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Midea 36000 too hot condenser and overload after few hours problem.

    60psi with R22 is a good suction pressure.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015