    Daikin REYQ14P8Y1B - VRV III - Address Issues



    Hello All,

    We have a site with a Daikin REYQ14P8Y1B - VRV III , connected to 11x Floor Mounted Units, BC Box's ( BSVQ16OPV1) and one I touch centralised controller ( controller also controls 1x VAM Unit - VAM1500FA8VE ) - installed in 2008.

    Due to refurbishment of the site we have had to remove one of the floor mounted units from the circuit. The unit removed was 1 of 4 units controlled via 1 BC Box.

    Having removed the unit and pipework we have now pressure tested and recharged. On trying to run the unit we constantly get a U4 error - Communication Error ( before the unit was removed all worked well)

    We have performed a system reset from the condenser but still the U4 error appears.

    The centralised controller is still showing the removed unit , could this be the issue??

    Any help would be appreciated.

    Thanks in advance



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Daikin REYQ14P8Y1B - VRV III - Address Issues

    have u done the wiring check function on the outdoor when you repowered it back up?
    also delete the removed indoors off the i touch

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Daikin REYQ14P8Y1B - VRV III - Address Issues

    did you drive the valves open when you pressure tested and vacced?

  4. #4
    Join Date
    Jul 2006
    Location
    essex
    Posts
    31
    Rep Power
    0

    Re: Daikin REYQ14P8Y1B - VRV III - Address Issues

    Hello install monkey , yes to the wiring check and yes to vales , would you have any literature on how to remove the unit from the I Touch controller ?

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Daikin REYQ14P8Y1B - VRV III - Address Issues


  6. #6
    Join Date
    Jul 2006
    Location
    essex
    Posts
    31
    Rep Power
    0

    Re: Daikin REYQ14P8Y1B - VRV III - Address Issues

    Thank you install monkey

  7. #7
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    48
    Posts
    186
    Rep Power
    20

    Re: Daikin REYQ14P8Y1B - VRV III - Address Issues

    You can also connect a service checker and delete the removed unit and reconfigure the system.

  8. #8
    Join Date
    Feb 2013
    Location
    Ukraine
    Age
    41
    Posts
    17
    Rep Power
    0

    Re: Daikin REYQ14P8Y1B - VRV III - Address Issues

    Quote Originally Posted by PRESS View Post
    You can also connect a service checker and delete the removed unit and reconfigure the system.
    Could you explain me, please, the way how can I remove unit from the system and configure it by using service checker?