09-08-2014, 09:12 PM #1
plate chiller refrigerant recovery
Hi guys ,Have to recover charge out of a small plate water chiller (14kgs) to repair a leak.System has no receiver and nowhere to recover liquid directly .Water will be running through exchanger at about 20c.Just still a bit worried about freezing in plate .Can any of you guys that have done this regularly offer any advice.
09-08-2014, 09:24 PM #2
Re: plate chiller refrigerant recovery
Why should the refrigerant recovery cause any problems?
It is being removed from the system, not flowing around the system.Brian - Newton Abbot, Devon, UK
09-08-2014, 09:29 PM #3
your water is circulating-at 20 deg so no issues
09-08-2014, 09:32 PM #4
Its a plate chiller , there will be liquid trapped in the plate boiling off .The question im kinda asking is if the water is running through the system is ok to just recover full out or will i have to recover down to the freezing point and stop and let the liquid boil off above freezing point.
09-08-2014, 09:36 PM #5
Sorry install was typing as you posted ,last post should have come out under brians,
09-08-2014, 09:37 PM #6
youve got a constant heat load, so no issues- if you wanted can you isolate the plate (water side) and drain it if your really worried- or disconnect the compressor,power up the chiller and moniter the flow ,return water temps
09-08-2014, 09:44 PM #7
id be more worried about draining it in case there is any still water trapped in it .Amazing ,ive been around a while but never came across a water chiller before . Are we ever finished learning in this job.
09-08-2014, 10:28 PM #8
10-08-2014, 04:12 AM #9
This is what im looking for .The machine is a cooling system on a laser lathe . If i pull the charge quick when theres 20c water has anybody seen ice to form in the exchanger.
10-08-2014, 08:56 AM #10
10-08-2014, 01:54 PM #11
Also be careful when charging the system back up, till its above 0c saturation pressure.