    plate chiller refrigerant recovery



    Hi guys ,Have to recover charge out of a small plate water chiller (14kgs) to repair a leak.System has no receiver and nowhere to recover liquid directly .Water will be running through exchanger at about 20c.Just still a bit worried about freezing in plate .Can any of you guys that have done this regularly offer any advice.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: plate chiller refrigerant recovery

    Why should the refrigerant recovery cause any problems?

    It is being removed from the system, not flowing around the system.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: plate chiller refrigerant recovery

    your water is circulating-at 20 deg so no issues

  4. #4
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: plate chiller refrigerant recovery

    Its a plate chiller , there will be liquid trapped in the plate boiling off .The question im kinda asking is if the water is running through the system is ok to just recover full out or will i have to recover down to the freezing point and stop and let the liquid boil off above freezing point.

  5. #5
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: plate chiller refrigerant recovery

    Sorry install was typing as you posted ,last post should have come out under brians,

  6. #6
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: plate chiller refrigerant recovery

    youve got a constant heat load, so no issues- if you wanted can you isolate the plate (water side) and drain it if your really worried- or disconnect the compressor,power up the chiller and moniter the flow ,return water temps

  7. #7
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: plate chiller refrigerant recovery

    id be more worried about draining it in case there is any still water trapped in it .Amazing ,ive been around a while but never came across a water chiller before . Are we ever finished learning in this job.

  8. #8
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: plate chiller refrigerant recovery

    Quote Originally Posted by joe-ice View Post
    id be more worried about draining it in case there is any still water trapped in it .Amazing ,ive been around a while but never came across a water chiller before . Are we ever finished learning in this job.
    If it has not been said already, keep the 20 deg C water flowing at all times & no problems if possible.

  9. #9
    Join Date
    Dec 2007
    Location
    ireland
    Age
    54
    Posts
    275
    Rep Power
    26

    Re: plate chiller refrigerant recovery

    This is what im looking for .The machine is a cooling system on a laser lathe . If i pull the charge quick when theres 20c water has anybody seen ice to form in the exchanger.

  10. #10
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: plate chiller refrigerant recovery

    Quote Originally Posted by joe-ice View Post
    This is what im looking for .The machine is a cooling system on a laser lathe . If i pull the charge quick when theres 20c water has anybody seen ice to form in the exchanger.
    Only if you do not keep water circulating

  11. #11
    Join Date
    Aug 2006
    Location
    england
    Age
    49
    Posts
    3,874
    Rep Power
    46

    Re: plate chiller refrigerant recovery

    Also be careful when charging the system back up, till its above 0c saturation pressure.