    Wink Daikin a0 fault



    Hi
    has anyone ever came across this fault code on a water cooled vrv4 system with only two hydro boilers connected



  2. #2
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: Daikin a0 fault

    This could be an error in the external protection device or activation of the external protection device or an improper field setting. It could depend where the flow switch has been connected.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  3. #3
    Join Date
    May 2008
    Location
    dublin
    Posts
    80
    Rep Power
    16

    Re: Daikin a0 fault

    What would be classed as a external protection.the flow switch is connected through 3 and 4 on the condenser.

  4. #4
    Join Date
    Dec 2008
    Location
    UK
    Posts
    568
    Rep Power
    24

    Re: Daikin a0 fault

    Maybe a fire alarm interlock or remote time-switch possibly. Possibly a high/low water temperature stat. Electrical interlock with external pump contactor maybe.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.