Thread: Daikin a0 fault
    May 2008
    dublin
    80
    Wink Daikin a0 fault
    has anyone ever came across this fault code on a water cooled vrv4 system with only two hydro boilers connected
    Dec 2008
    564
    Re: Daikin a0 fault
    This could be an error in the external protection device or activation of the external protection device or an improper field setting. It could depend where the flow switch has been connected.
    Bedford. Now retired and trying to relax.
    May 2008
    dublin
    80
    Re: Daikin a0 fault
    What would be classed as a external protection.the flow switch is connected through 3 and 4 on the condenser.
    Dec 2008
    564
    Re: Daikin a0 fault
    Maybe a fire alarm interlock or remote time-switch possibly. Possibly a high/low water temperature stat. Electrical interlock with external pump contactor maybe.