    Carrier Aquasnap 30RH
    Few questions:
    We have here a Carrier 30RH type with a pro-dialog junior interface running in local mode.
    *Can this specific water chiller cool below the default 10°C? If so, what needs to be changed to
    accomplish this. We want the unit cool the water close as possible to the freezing point without freezing the heat-exchanger. (2-4°C)
    *What value in the service menu needs to be changed to change the unit to "Leaving water temperature control"
    *How the load function works and how to set it. At the moment its cooling between 8-12°C (needs to be 2-4°C) and we like to cool it more accurate with a target of 2-3°C
    (If anyone can PM me a list of the service function/description I appreciate it)
    Regards,
    Harry
    ireland
    1,451
    41
    Re: Carrier Aquasnap 30RH
    http://www.mediafire.com/view/0njq5n...(operator).pdf
    you'll need password to access, might be safer to get your maintenance company to make changes, unless you are an engineer?
    Auckland
    74
    3,357
    38
    You will have to add glycol to system to achieve +2' > 4C leaving water.
    Aug 2014
    netherlands
    2
    The manual I've found already, thanks anyway, but the settings needed to be changed are under the service menu, which are note listed in the manual of course.
    No, I'm not a Engineer, but relaying info. The engineer in question is unfamiliar with the unit.