    Industrial Style HG Bypass Valve Question



    This valve is being used as a hot gas bypass on an air conditioning system. The 1/4" tubing on the right - what pressure should that be connected to? Does it need to be run all the way back to the compressor or can be tied in near the evap coil?
    Thanks
    Attached Images Attached Images



  2. #2
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    336
    Rep Power
    21

    Re: Industrial Style HG Bypass Valve Question

    Is this it?

    http://www.parker.com/literature/Lit...LS/DN23-07.PDF

    Note the flange ring - usually located on valve outlet.

  3. #3
    Join Date
    May 2012
    Location
    Canada
    Posts
    2
    Rep Power
    0

    Re: Industrial Style HG Bypass Valve Question

    That certainly looks a lot like the valve that I have. There must be numbers on it somewhere but I haven't been able to see anything yet. It is in a bad spot, I'll check again. The main question was where that monitor line had to be hooked up. Whoever installed this valve ran it all the way back to the compressor, I suppose that would be to have a more accurate reading of what's going on with the suction pressure and to get away from where the hot gas is being injected in the evap coil.

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Industrial Style HG Bypass Valve Question

    You may not find any markings on valve except if there is something it's on a tag on top part of valve like A4A port 3/4 or 1" for a 2 bolt valve like this.
    i cannot see any reason pilot has to run back near compressor suction, unless there is another pressure regulator or control valve in the line between it & compressor.
    It's basically a false load valve to keep compressor running.

    Can you explain system a bit more so we understand it.
    Last edited by RANGER1; 08-08-2014 at 08:52 AM.

  5. #5
    Join Date
    Oct 2007
    Location
    New Zealand
    Age
    51
    Posts
    52
    Rep Power
    17

    Re: Industrial Style HG Bypass Valve Question

    It is dependant on the required function of the valve. Does this go into a distributor upstream of an EXV?

  6. #6
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Industrial Style HG Bypass Valve Question

    That's an old one. The mounting of the solenoid passing the pilot stream piped such that the solenoid body is a separate piece from the adapter on the regulator went away with the introduction of Modudapter valves in something like 1974. That big cast solenoid coil cover went away before that.....
    So actually this could be an A4COES or an A4AOES. Either way: the question tubing needs to be equalized to the pressure you are trying to manage, and if its false loading the compressor with no hold back type devices between the compressor and the evap then the evap suction is fine. If there is more than one evap to this specific bank of evaporators it can be marginally more complicated than that but there is still no need to take it back to the compressor