    Unhappy old r12 walk in freezer won't drop below 3*.



    Sight glass is clear. Superheat at compressor is 20*. Both coils clean. It's an old semi hermetic, I thought the valve plate was bad. Changed out the valve plate expecting a super efficient compressor, but got no improvement. Not familiar with r12, I think the suction was at like 12 psi, witha bout 10* box temp. The damn thing runs and runs.



  2. #2
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: old r12 walk in freezer won't drop below 3*.

    What state is the condensor at?, what is the ^t on the filter dryer?

    TXV or Cap. so much info missing here
    Now in Redvers Sask.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: old r12 walk in freezer won't drop below 3*.

    Superheat at evaporator? Frost pattern at evaporator?

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: old r12 walk in freezer won't drop below 3*.

    Why are you working with/on R12 ????
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: old r12 walk in freezer won't drop below 3*.

    Door seals? cold room panels ok?
    Mostly found in Oxfordshire, UK :)

  6. #6
    Join Date
    Mar 2010
    Location
    australia
    Age
    56
    Posts
    5
    Rep Power
    0

    Re: old r12 walk in freezer won't drop below 3*.

    Quote Originally Posted by jasonrd View Post
    Sight glass is clear. Superheat at compressor is 20*. Both coils clean. It's an old semi hermetic, I thought the valve plate was bad. Changed out the valve plate expecting a super efficient compressor, but got no improvement. Not familiar with r12, I think the suction was at like 12 psi, witha bout 10* box temp. The damn thing runs and runs.
    What head pressure do you have?

  7. #7
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: old r12 walk in freezer won't drop below 3*.

    you sure its a freezer, not a fridge

  8. #8
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: old r12 walk in freezer won't drop below 3*.

    How long has the box been offline? What is the insulation like? If it has completely thawed and then the insulation has got wet, it will take a long time to re-freeze the insulation. As it was designed for R12 and is therefore probably quite old, you would be lucky to get down to 3degF or are you meaning 3degC? What are the suction and head pressures, is it fully or over charged. Have you got any restrictions at the drier?
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  9. #9
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: old r12 walk in freezer won't drop below 3*.

    One hit wonder, think it safe to say no need for futur rplies here till they can be bothered to post above stated data.
    Now in Redvers Sask.