    Daikin packaged unit evaporator icing



    Hi All. Need some help. I have a Daikin unit model RUR15NY1 (outdoor unit) and FDR15NY1 (indoor unit) using R410A. I am having icing issues. My steps so far:-

    1) after finding the evaporator coil fully iced, i turned off the system for a day.
    2) turned on the unit on day 2 and checked. No more icing at evaporator but suction pipe and accumlator at condenser side is totally iced. set temperature able to achieve. Checked low side pressure is 90psi and high side is 380psi. I did not charge anymore gas because the suction pipe and accumulator are already icing.
    3) The running amp is at 27A, very close to the max rated which is 26.4A. Therefore not adviseable to charge further gas.

    So now i need the HVAC gurus to tell me what i should do next. BTW i am from Asia where the average ambient temperature is from 25 celcius to 35 celcius with humidity around 80 to 90RH.



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Daikin packaged unit evaporator icing

    Joe,
    Suction is below 0 deg C
    check clean indoor unit filter & coil if necessary, check airflow
    check condenser is clean & airflow

  3. #3
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    48
    Posts
    184
    Rep Power
    20

    Re: Daikin packaged unit evaporator icing

    Is this a new or existing installation? If its new you may have to check your piping lengths and recalculate the amount of additional gas. As ranger has indicated you are running below 0DegC. If it is an existing installation then you have to follow ranger's recommendations above.

  4. #4
    Join Date
    Oct 2013
    Location
    singapore
    Posts
    11
    Rep Power
    0

    Re: Daikin packaged unit evaporator icing

    Quote Originally Posted by PRESS View Post
    Is this a new or existing installation? If its new you may have to check your piping lengths and recalculate the amount of additional gas. As ranger has indicated you are running below 0DegC. If it is an existing installation then you have to follow ranger's recommendations above.
    Mine is an existing installation. I did cleaning earlier on evaporator air filters, coil and condenser coils. I am suspecting 2 things

    1)maybe the evaporator coil is choked causing low heat exchange
    2) Thermal expansion valve not operating properly. Is there a way to check it?

  5. #5
    Join Date
    Aug 2014
    Location
    Australia
    Age
    36
    Posts
    68
    Rep Power
    10

    Re: Daikin packaged unit evaporator icing

    Check your airflow, as above threads have stated.
    If your fan motor is not running (faulty capacitor or belt has broken) then you will have a complete ice down of the suction line etc, because there is no heat rejection.

  6. #6
    Join Date
    Oct 2013
    Location
    singapore
    Posts
    11
    Rep Power
    0

    Re: Daikin packaged unit evaporator icing

    hi all

    my airflow at evaporator is good. in fact I removed the air filter and ran the system and here is the diagnosis-
    suction pressure 95psi
    liquid side pressure 350psi
    compressor running amps 30A (max rated 26.4A)
    no more icing noticed in first 4hrs. I placed back another filter from another unit and monitoring for next few days.

    But here are my questions-
    evaporator side temperature is below 0deg C. is it good or not.
    compressor running amps is over and above rated amps. ok or not