    Hi all been to look at a twin searle evap system on a old prestcold unit the unit furthest away start to frost back heavily after checking gas pressures at condensor all seem ok i am wondering if the tev maybe open too much but i couldnt check anyrhing due to the factory being in production any advice is very welcome
    3,853
    Re: searle twin evap
    Check the coil is clean, and free of frost. You can still check the superheat at the compressor, will give you a pointer to whats going on.
    Is it a chiller or a freezer?
    Feb 2009
    telford
    2,090
    33
    could be numerous faults think i would start at the one thats not iced the fault maybe with that one possible restriction causing the other to do too much work?
    Mar 2011
    34
    101
    14
    Everhthing seems fine its 2 twin discharge air evaps but the furthest one away frosts over the coil not alot but enough to cause concern they have been using a hot pressure washer under it but it got isolated and hasnt made a difference
    Mar 2011
    34
    101
    14
    Went back to the system pressure washed all 3 evaos found 1 of them losing heat through the liquid line the other 2 evaps are pretty even temp right across its only the 1 would i be right im thinking the tev is u/s
    Apr 2006
    41
    1,620
    Grab on the TXV bulb with your hand and see if it responds by oppening, doesw it open? if a solenoid valve pressent does it ice up?
    if there is a way to isolate the evap you can dismantle the valve and give the internals a cleaning and lubricate with clean oil then re-assemble and test again, if valve responds then issue would be the distrobuter for the evap may be clogged with debree.
    All so befor any thing make sure the bulbe is firmly clamped the pipe at the correct possition! some times the simplist is the problem!
    Now in Redvers Sask.
    Mar 2011
    34
    101
    14
    It was the tev at fault on the unit that were doing sweet fa help hand uver bulb and not a sausage pumped down remove replace valve all food it looks as if the pin in the old valve has stuck in position