    Hi all,

    I've recently had an MSZ-FH35VE fitted in a fairly small room. It's great - but when I set it to a temperature it can reach easily and close the door, it stops cooling pretty quickly and then blows damp-smelling air around the room, making the atmosphere unpleasant.

    Is there a way to make the fan shut down when cooling isn't needed? When it's cooling, the smell is lovely and crisp, but I don't want to freeze myself in order to achieve that!

    Thanks

    Stephen



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Damp smell from air conditioner when running but not cooling

    Quote Originally Posted by stephenM View Post
    Hi all,

    I've recently had an MSZ-FH35VE fitted in a fairly small room. It's great - but when I set it to a temperature it can reach easily and close the door, it stops cooling pretty quickly and then blows damp-smelling air around the room, making the atmosphere unpleasant.

    Is there a way to make the fan shut down when cooling isn't needed? When it's cooling, the smell is lovely and crisp, but I don't want to freeze myself in order to achieve that!

    Thanks

    Stephen
    That should not happen.
    Was it installed professionally? If so get them back to look at it.

    If it is smelling then it could be sucking air from the drain?

    It could be a multitude of reasons but it should not happen.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Aug 2014
    Location
    UK
    Posts
    8
    Rep Power
    0

    Re: Damp smell from air conditioner when running but not cooling

    Hi Rob,

    It was commissioned professionally but I installed the components. I've had it running this evening keeping the temp at 24c, door closed and the atmosphere is bad enough to keep you out of the room. It's a kind of musky smell, not damp exactly but just really unpleasant. Humidity is kept pretty much constant at 60%, which doesn't seem to fit in with how awful the air is. It makes my lungs feel all furry and like I shouldn't be breathing it in.

    I installed the condensate drain pipe over quite a long distance - around 7 meters (I want to collect the water in a waterbutt in the back garden). It does drain, but in places the pipe is at quite a shallow angle - I wonder whether that could be causing the condensate tray to not drain fast enough?

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Damp smell from air conditioner when running but not cooling

    Have you fitted a water trap in pipe before it empties into the water butt?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Aug 2014
    Location
    UK
    Posts
    8
    Rep Power
    0

    Re: Damp smell from air conditioner when running but not cooling

    Hi Brian,

    Quote Originally Posted by Brian_UK View Post
    Have you fitted a water trap in pipe before it empties into the water butt?
    No - should I have?

  6. #6
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: Damp smell from air conditioner when running but not cooling

    It could potentially be drawing the stale water smell from the water butt back up the drain tube.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  7. #7
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    49
    Posts
    184
    Rep Power
    20

    Re: Damp smell from air conditioner when running but not cooling

    Drains are the usual suspect for foul air in most cases like this. Make sure you have a drain trap on your condensate drain piping as advised above. check if there is no dust of other things on the coils, fan blades and drain tray which may potentially be generating this foul smell.

    Regarding the fan and the amount of air blowing you can simply manualy select the air speed from your remote controller. I hope this will help.

  8. #8
    Join Date
    Nov 2008
    Location
    scunny!
    Age
    35
    Posts
    302
    Rep Power
    22

    Re: Damp smell from air conditioner when running but not cooling

    Put a smelly jelly in it

  9. #9
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Damp smell from air conditioner when running but not cooling


  10. #10
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Damp smell from air conditioner when running but not cooling

    I'm not surprised, it looks like it's in a bakery or something similar?

    Bakeries are bad environments for coils.

    Regards

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  11. #11
    Join Date
    Nov 2008
    Location
    scunny!
    Age
    35
    Posts
    302
    Rep Power
    22

    Re: Damp smell from air conditioner when running but not cooling

    Never knew fascias came in sticky brown

  12. #12
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Damp smell from air conditioner when running but not cooling

    You mention this is a 3.5kw installed in a fairly small room. Seems like the unit is oversized, you also mention that it reaches temperature quickly and then cycles off. Can you advise of room measurements and any other heat loads in the room eg south facing etc.

    I've heard of this before... the issue is because the unit starts cooling the coil gets nice and wet absorbing any smells in the room, normally with the system running the coil keeps getting wetter and wetter and any contaminants in the room get flushed through and out the drain but in your case because it isn't running the cooling cycle long enough due to being oversized the compressor cannot respond quick enough to ramp down so it just cycles off. That moisture then evaporates back of the coil and you get a musty smell sometimes almost sweaty smell as its the smells that are left behind.

    You need to either call back the installer as its oversized for the room or perhaps you need to run on a low fan speed so that the unit is able to generate enough condensate to rinse the coil through - the outdoor then may be able to ramp down.

    A test you could try is set the set point to the lowest setting, then make sure the unit runs for an hour, after this set the set point to a comfortable setting and yes you will get the usual smell of moisture evaporating off the coil but there shouldn't be any bad smells associated with it. Also ensure there is adequate ventilation in the room e.g a window on the catch or internal doors open as these things recirculate any smells in the room be it cooking, breathing & sweating or farting will be pulled through the a/c and onto the coils.

  13. #13
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Damp smell from air conditioner when running but not cooling

    Try running it in drying mode and see if it is any better, sounds oversized. Did you buy it yourself and then get it installed?
    Mostly found in Oxfordshire, UK :)

  14. #14
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Damp smell from air conditioner when running but not cooling

    Oversized kit. Is there carpet? Heavy curtains? Animals in the house? A/C runs a short cycle and keeps humidity too high. Recycled air in these conditions causes bad smells.

    Ah... re-read comments and "back2space" on post #12 has already said it better than me
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  15. #15
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Damp smell from air conditioner when running but not cooling

    the drain you ran should have a constant fall of 1 cm per mtr, as others have said a u trap will stop smells but if your water butt doesnt stink then the u trap wouldnt be req,
    if its a small room,why did they fit a 3.5kw and not a 2.5??
    run the unit in heating for a while- does it smell of cat piss?? your coil will need cleaning

    have u tried the fan in auto mode- will slow down when at setpoint

  16. #16
    Join Date
    Jan 2014
    Location
    Uk
    Age
    40
    Posts
    91
    Rep Power
    12

    Re: Damp smell from air conditioner when running but not cooling

    Haha I love trying to come up with a better explanation than cat piss to a customer, but that's it cat piss

  17. #17
    Join Date
    Nov 2008
    Location
    scunny!
    Age
    35
    Posts
    302
    Rep Power
    22

    Re: Damp smell from air conditioner when running but not cooling

    Quote Originally Posted by Anz View Post
    Haha I love trying to come up with a better explanation than cat piss to a customer, but that's it cat piss
    "musty smell"

  18. #18
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Damp smell from air conditioner when running but not cooling

    Quote Originally Posted by jonjon View Post
    "musty smell"
    Sweaty socks or damp towels!

  19. #19
    Join Date
    Jan 2014
    Location
    Uk
    Age
    40
    Posts
    91
    Rep Power
    12

    Re: Damp smell from air conditioner when running but not cooling

    Nah it's definitely cat piss haha

  20. #20
    Join Date
    Aug 2014
    Location
    United States
    Age
    44
    Posts
    2
    Rep Power
    0

    Re: Damp smell from air conditioner when running but not cooling

    Yes that's right a very bad smell comes from air conditioner when the room temperature is equal to the set temperature. We can use the air freshener for this purpose.

  21. #21
    Join Date
    Oct 2008
    Location
    North East
    Posts
    1,050
    Rep Power
    19

    Re: Damp smell from air conditioner when running but not cooling

    It's air fresheners that actually contribute to the bad smell in the first place as they are sucked in and mixed with other odours.

  22. #22
    Join Date
    Jan 2014
    Location
    Uk
    Age
    40
    Posts
    91
    Rep Power
    12

    Re: Damp smell from air conditioner when running but not cooling

    Yeah, u usually find there's sum1 sat under the a/c covering themselves in perfume or tins of lynx at once

  23. #23
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Damp smell from air conditioner when running but not cooling

    usually the female who's past their best- usually in accounts or hr dept!- and theyre trying to describe the smell- they never shout cat piss- i do! haha- mate used grease gobbler on an mitsi evap- melted hole in drip tray! haha

  24. #24
    Join Date
    Aug 2014
    Location
    United States
    Age
    44
    Posts
    2
    Rep Power
    0

    Re: Damp smell from air conditioner when running but not cooling

    Quote Originally Posted by Anderson245 View Post
    Yes that's right a very bad smell comes from air conditioner when the room temperature is equal to the set temperature. We can use the air freshener for this purpose.
    any comment?

  25. #25
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: Damp smell from air conditioner when running but not cooling

    ya, fix the problem don't mask it. perfumes and such are an environmental toxin, not a repair.